AE-Gifts, Affordable Everyday
0 members (), 417 guests, and 8 robots.
#76286 01/09/01 10:52 PM
doc Offline OP
I have to hook up a piece of equipment that is 3 phase 220 volt and pulls 22 amps ,problem the circuit that runs by it is in 1 inch EMT and has 16 #10 thhn wires in it 3 of which are suppossed to go to the equipment .This run is also roughly 250 feet long ,am I correct by looking at the derating chart and at 10 - 20 conductors I derate to 50 percent and can only load 15 amps on these wires ? or am I only allowed 80 percent of the 50 percent which would be 12 amps ? not for sure which it is but have 1 red wire that is being used for a grounded conductor or a neutral
Workgear for Electricians
#76287 01/10/01 12:19 AM
Doc,
If all the conductors are current carrying, then you can figure all 16 of them at 50% of the maximum rated ampacity. Derating is 10 to 20 current carrying conductors to be 50% of maximum rating of conductors.
310-16 shows 35 amps for #10 THHN cu, so 50% of that is 17.5 amps. If you step up to the next higher device rating, that places all conductors on a 20 amp max breaker or fuse.
17.5 amps is the maximum amperage that would be flowing through each of these conductors at one time. If the load is less than or up to 17.5 amps on any conductor, that is OK and can be protected by a 20 amp C/B [even a 30 amp C/B, but that's a little out there]. Protecting the branch circuit with a 15 amp breaker would limit the maximum that could be drawn to at least 15 amps.
Looks like since you have shown 22 amps in your message you will need to either upgrade the conductors for the equipment you are installing to #8 cu, or run a new branch circuit.
Since it is so long, you are better off running a new branch circuit with #8 THHN cu, to overcome the voltage drop of #10s, unless you have figured the volts lossed at 22 amps is not too bad with #10 [seems like it would be excessive just offhand, but maybe it's not].
There will definitely be an excessive voltage drop if all the conductors in that 1" EMT are loaded plus continuous. That will create quite a bit of heat.
If the equipment is to run for 3 hours or more, then do the normal LCL adder to the branch circuit [load]. Either multiply the FLA by 1.25 [add 125%], or derate the circuit's maximum load by 80% and see if the motor load falls in there. Much simpler to add 125% to the total motor load calc [FLA + 125% motor factor, or the listed Min. Ckt Amperage].
Good luck.
Scott.
#76288 01/10/01 03:56 PM
doc Offline OP
scott,I took the 22 amps off of the machine control panel it is stamped fused disconnect 30 amps and equip full load is 22 amps,being in a mfg. plant I have to consider all of those #10s are going to be full load at some point
#76289 01/10/01 08:29 PM
doc,
I would go with Scott's suggestion to run a new circuit (#8's) Using the existing wiring at that load could even have some detrimental effect on equipment connected to the other wiring as well. You have to remember that all circuits inside the conduit are affected by each other when it comes to heat.