Metal Clad Cable #76125 12/14/00 10:11 AM
Joined: Dec 2000
Posts: 84
C
cinkerf Offline OP
Member
What is the best way to determine if the sheath of metal clad cable is suitable for equipment grounding. (Frank) cinkerf

2017 / 2014 NEC & Related Books and Study Guides
Re: Metal Clad Cable #76126 12/14/00 08:42 PM
Joined: Dec 2000
Posts: 127
G
gpowellpec Offline
Member
Go to http://www.afcweb.com./ and enroll in their online learning program. It doesn't take long. AFC manufactures MC cable.

Re: Metal Clad Cable #76127 12/14/00 09:52 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
It looks to me that MC armor by itself is not approved for Grounding. But AC armor w/strip is.

Table at: http://www.afcweb.com./groundcp.html


Bill
Re: Metal Clad Cable #76128 12/15/00 08:28 AM
Joined: Dec 2000
Posts: 84
C
cinkerf Offline OP
Member
I located section 250.18(8)(11) "The metallic sheath OR the combined metallic sheath and grounding conductors of type MC cable". It falls under Types of Equipment Grounding Conductors. If read word for word it seems as if the sheath of MC cable would be suitable for an equipment grounding method. (Frank) cinkerf

Re: Metal Clad Cable #76129 12/15/00 08:31 AM
Joined: Dec 2000
Posts: 84
C
cinkerf Offline OP
Member
Correction. That is section 250.118(8)(11)

Re: Metal Clad Cable #76130 12/15/00 09:08 AM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Frank,

You got me wondering what's going on then. If you look at AFC's FAQ page it lists some Qualities of the MC cable types


"The difference between HCF and MC cables (as manufactured by AFC Cable Systems) is the grounding capabilities of the cable assemblies.

Type HCF cable has a green grounding conductor plus the armor/bond wire combination, thereby providing redundant or isolated grounding capability. HCF is a Type AC cable and is manufactured in accordance with U.L. 4.

HCF cable may be installed in compliance with NEC 517 for health care facilities.

Type MC has only one equipment grounding means, a green grounding conductor. There are types of MC cable manufactured by AFC with two grounding conductors for additional grounding capability."

This is from page: http://www.afcweb.com./faq.html
and would seem to indicate that it is not approved for Grounding. I can see why you're questioning it.


Bill
Re: Metal Clad Cable #76131 12/15/00 12:05 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
The UL White Book indicates that the interlocked metal tape sheath is NOT suitable as a grounding conductor and an insulated or bare EGC will be provided. It also says that "the sheath of the smooth or corrugated tube Type MC calbe or a combination of the sheath and a supplemental bare or green insulated conductor is suitable for use as the required EGC".
Don(resqcapt19)


Don(resqcapt19)
Re: Metal Clad Cable #76132 12/15/00 03:42 PM
Joined: Dec 2000
Posts: 84
C
cinkerf Offline OP
Member
Don,
In the margin of section 250.118(8)(11) there is a verticle line which indicates a code change from the previous (1996) NEC. It does not specify smooth or interlocked metal sheath. It simply states type MC cable. I would have to agree with you based on your findings in the UL White Book.
(Frank) cinkerf


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 1
Popular Topics(Views)
271,002 Are you busy
205,005 Re: Forum
193,123 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3