ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Inspection camera help
by Bill Addiss. 09/19/18 10:50 PM
220/230/240V 60Hz Systems
by gfretwell. 09/16/18 12:37 PM
Acronis Backup 2017
by gfretwell. 09/16/18 12:46 AM
Tingle off the water spigot
by Trumpy. 09/15/18 03:24 AM
Lighting Load questions
by HotLine1. 09/14/18 07:04 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
1 registered members (Bill Addiss), 27 guests, and 21 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Subpanels fed from Transformer-SDS #76108
12/09/00 03:18 PM
12/09/00 03:18 PM
Scott35  Offline
OP
Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Got a few design issue questions to post, in order to get some feedback. Has to do with separately derived systems [SDS].

Example: Two [2] 225 amp subpanels for 208y120 3 phase 4 wire power fed from a 150 KVA 480 / 208Y120 3 ph 4 wire step down Transformer. Z% = 2.0%. Subpanels located within 25 linear feet of transformer and all equipment is in one common room. For the sake of argument, we will say the max SCA is 24 KAIC.

Would like your input [code related, personal preference and cost wise] to the Secondary Overcurrent Protection and disconnects, plus preferred Primary Protection.

My example would have the subpanels run with 250 MCM THHN cu, and each to have a main OCPD rated at 225 amps, 42 KAIC. From the Transformer, a fused switch with 3-400 amp RK-5 [200KAIC] fuses and paralleled 250s-300 MCM cu. Time-current curves to allow selectivity between branch C/Bs, Main C/B and finally the 400 amp fuses.
Primary to be protected via 175/3 Circuit Breaker with a AIC rating of, like 65,000 [or next step above what ever is available at the gear] and fed via 3-4/0 THHN cu.
Grounding connected via common grid connections.

Please reply with your opinions, questions, suggestions and such. This is an example situation only. It is only posted for a conversation piece [Linked Image].

Scott. "S.E.T."

P.S. I hope these "design" example ideas are OK with the group. Just trying to get something going here and there and to see the various answers/comments.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
2017 / 2014 NEC & Related Books and Study Guides
Re: Subpanels fed from Transformer-SDS #76109
12/10/00 01:05 AM
12/10/00 01:05 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The primary breaker seems small. The primary fla should be 180 amps and protection could be as much as 250% of this per Table 450-3(b). It may be more cost effective to provide 2 225 amp breakers on the secondary at the transforemer in place of the 400 amp fused disconnect and the 225 amp main breakers in the panels. The secondary of the transfromer will require a grounding electrode system per 250-30(a)(3). The common grounding grid may not meet this requirement.
Don(resqcapt19)


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 9
Popular Topics(Views)
249,297 Are you busy
187,231 Re: Forum
176,594 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.005s) Memory: 0.9446 MB (Peak: 1.0621 MB) Zlib enabled. Server Time: 2018-09-20 04:52:10 UTC