Allowable voltage drop in DC Circuits #75983 03/23/07 03:23 PM
Joined: Jan 2006
Posts: 47
N
NJ_WVUGrad Offline OP
Member
I am working under the assumption that DC circuits fall under the maximum 3% allowable voltage drop as stipulated by the NEC.


Is this correct?

It is for DC feeds to radio equipment located on the roof of a building being fed from rectifers in the basement.

Work Gear for Electricians and the Trades
Re: Allowable voltage drop in DC Circuits #75984 03/23/07 03:50 PM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
NEC never actually requires 3%, just recommends it. I'd put this into the category of "it's always a good idea to oversize for voltage drop" though!

What's the acceptable DC voltage range of the equipment? If it can handle the drop, it's not a big deal.

Re: Allowable voltage drop in DC Circuits #75985 03/23/07 03:54 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
I agree with Steve, great idea to maintain less than 3% but not NEC required.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Allowable voltage drop in DC Circuits #75986 03/23/07 06:54 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
NJ:
This was a class 'discussion' item last nite.

Vd is a fpn (Fine Print Note), not 'Code' not mandatory.

Vd is a design issue, and could/may be debated via 110.3 (B)

'Good Practice' & 'Common Sense' are not in the NEC, but should be observed by all.

I would check the equipment for a voltage, and take a reading under load, if it's already installed. Or, I would do the calcs on paper beforehand, and 'lean' to a larger conductor.

John


John
Re: Allowable voltage drop in DC Circuits #75987 03/23/07 08:40 PM
Joined: Jan 2006
Posts: 47
N
NJ_WVUGrad Offline OP
Member
Thanks for the input,

Now that everyone mentions it I remember this coming up in past.

The equipment runs 48vdc and the equip manufacturer states that the equip is fully operational down to 36vdc and they often crank up the output on the DC rectifiers to compensate.

I will just have to come up with allowable voltage drop calcs for these designs based on that criteria.

Thanks for the help

Re: Allowable voltage drop in DC Circuits [Re: NJ_WVUGrad] #160785 03/25/07 07:36 PM
Joined: Jan 2006
Posts: 47
N
NJ_WVUGrad Offline OP
Member
Just curious about others opinions,

Designing engineer for the clients wants us (the consulting engineers) to spec out pulling a Cat5e cable in the same 2" conduit with (6) #2AWG DC cables for the radio equipment.

This cable is simply an alarm cable that will tell them if the door on the Equipment cabinet is open or closed.

The cable pulls will be in the range of 200-400'.

Anyone have any tips for getting the Cat5 pulled in with the #2's without tearing it up


Re: Allowable voltage drop in DC Circuits [Re: NJ_WVUGrad] #160791 03/25/07 08:09 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
Back in the olden days when we were pulling fiber with other fat conductors in ducts we pulled it in innerduct, a smurf tube like deal. That may not be an option in 2" tho. You need to do a fill calc.


Greg Fretwell
Re: Allowable voltage drop in DC Circuits [Re: gfretwell] #160807 03/26/07 05:38 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
I see smurf tube all the time to protect the fiber optic cabling, but yeah, not an option. Mil-spec cat5 has a stronger jacket and would easily hold up, but it's expensive.

Why not just pull the cat5e in last?

Re: Allowable voltage drop in DC Circuits [Re: SteveFehr] #160810 03/26/07 06:16 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
If you have a couple of 90s, the Cat 5 is likely to be damaged or broken. We won't even install #14 control wires in with power wires larger than #4. This happens where there is a 90 near the end of the run. Some of the conductors will take the short path on the inside of the 90 and others will have to be a bit longer riding on the outside of the inner conductors. This extra length has to come from the feed end and if the Cat 5 is on the outside and if it can't slide by the other conductors it will stretch or break.
Don

Last edited by resqcapt19; 03/26/07 06:16 AM.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,641 Are you busy
209,564 Re: Forum
196,916 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3