Generator Interlock ? #75334
02/23/07 06:04 PM
02/23/07 06:04 PM
S
SparksNmore  Offline OP
Member
Joined: May 2005
Posts: 16
KC KS
Just curious, what’s your thoughts on the Generator Interlocks?

They don't look fail safe to me.
http://www.interlockkit.com/

Work Gear for Electricians and the Trades
Re: Generator Interlock ? #75335
02/23/07 07:21 PM
02/23/07 07:21 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Had a similar set-up on UPS system panelboards, but it was "factory" installed, not an aftermarket 'add in'

Mechanical type interlocks have been around for a long time.

This seems like a good idea for a manual transfer setup. Now I ask....is the backfed cb bolted down (or clipped)???

John


John
Re: Generator Interlock ? #75336
02/23/07 08:28 PM
02/23/07 08:28 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
John,
Quote
Now I ask....is the backfed cb bolted down (or clipped)???
you're a trouble maker aren't you? [Linked Image] [Linked Image]


Roger


[This message has been edited by Roger (edited 02-23-2007).]

Re: Generator Interlock ? #75337
02/23/07 08:55 PM
02/23/07 08:55 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Roger:
Now that comment I would expect from Bob (Iwire). Now where is George Little??

John


John
Re: Generator Interlock ? #75338
02/26/07 02:06 PM
02/26/07 02:06 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Even the high-dollar interlocks can be bypassed with a screwdriver. But we swear by them just the same- sure, I'd like to think nobody is stupid enough to close the tie breaker while the two halves of the switchboard are fed from separated sources, BUT...

So, yeah, I use a lot of interlocks but bypass a lot of interlocks during non-standard evolutions, too. Their purpose is not so much to force the "expert" into a certain sequence but moreso to protect the idiot from blowing something up. I don't have any experience with this brand, but it looks like it could easily save someone the cost of an MTS [Linked Image]

Re: Generator Interlock ? #75339
02/26/07 02:46 PM
02/26/07 02:46 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
Idiot proof is only good until the "better" idiot comes along.


Greg Fretwell
Re: Generator Interlock ? #75340
02/26/07 04:29 PM
02/26/07 04:29 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I'll be giving one of these a try in the next month or so. This interlock offers a few advantages that I can see, namely, my customer does not have to make up his mind which circuits he wants on a separate panel. This interlock is also going to be handy due to a lack of space to mount another panelboard.

That better idiot mentioned above probably lives here in the Mountain State. We seem to lead the nation in the bad categories & trail in the good ones.

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: Generator Interlock ? #75341
02/26/07 06:32 PM
02/26/07 06:32 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Tom:
I doubt that you have the market cornered in 'better idiots'.

John


John
Re: Generator Interlock ? #75342
02/26/07 07:16 PM
02/26/07 07:16 PM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
No doubt someone is going to try and defeat the interlock! Why? Someone will probably figure they can TRY and lower their electric bill if they have their generator running at the same time their panel is being supplied off mains power OR they don't want to have their lights go out for that split second when they transfer back from gennie supply to mains supply.
Trust me I know people that would want to do that.. All I say is " good luck" to them!

A.D

Re: Generator Interlock ? #75343
02/26/07 07:17 PM
02/26/07 07:17 PM
J
JCooper  Offline
Member
Joined: Dec 2002
Posts: 228
Kendall Park, NJ USA
Nothing is truly idiot proof, just idiot resistant

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,114 Are you busy
185,575 Re: Forum
174,887 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.036s Queries: 15 (0.005s) Memory: 1.0265 MB (Peak: 1.2044 MB) Zlib enabled. Server Time: 2018-07-18 16:44:16 UTC