ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Video door bell causing chime activation of coil
by gfretwell. 12/10/18 12:35 AM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Pull out fuse panel?
by Trumpy. 12/06/18 02:12 AM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
Tingle off the water spigot
by rmiell. 11/30/18 01:03 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 7 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
so cord #75291
02/20/07 09:00 PM
02/20/07 09:00 PM
H
highground  Offline OP
Member
Joined: Nov 2004
Posts: 53
Chama, NM
I have to install cords on some welders in a shop environment, with a high potential for abuse. What are my options other than so cord? I am not familiar with what might be available for such an application?
480V volt 60A and 480V 50A.

Thanks

Work Gear for Electricians and the Trades
Re: so cord #75292
02/21/07 09:47 AM
02/21/07 09:47 AM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
RMC!!!!

Larry C

Re: so cord #75293
02/21/07 09:50 AM
02/21/07 09:50 AM
I
IanR  Offline
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
There is Type-W power cable. It is very heavy duty and usually is rated for 2000V intead of 600V like SO.
This is the stuff the Military uses for their portable power distrubution in the field, so it must be able to stand up to considerable abuse. Here is a link to inw manufacture http://www.acewireco.com/pdfs/6401.pdf

[This message has been edited by IanR (edited 02-21-2007).]

Re: so cord #75294
02/21/07 10:50 AM
02/21/07 10:50 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Any 600 volt rubber cord will be fine.

I would want something like SEOO-W.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: so cord #75295
02/21/07 10:51 AM
02/21/07 10:51 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
One other thing, do not scrimp on the cord connectors or plug.

Kellem style cord grips at each end would make it last longer.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,163 Are you busy
189,155 Re: Forum
178,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9672 MB (Peak: 1.1054 MB) Zlib enabled. Server Time: 2018-12-12 12:01:09 UTC