# of conductors in conduit #74752
02/04/07 12:43 PM
02/04/07 12:43 PM
K
kyelectric  Offline OP
Member
Joined: Aug 2005
Posts: 64
No matter what the size of the conduit, you always have to derate the conductors accordingly when you have over 3. Correct? So, like most people think, "put a bigger size conduit in and you can pull more wires!" For instance, putting 1/2" EMT in limits the # of conductors that can be pulled because of it's size. But really, even if I put a 1" EMT conduit in I can fit more conductors in but I have to start derating at 4-7 conductors. So even if I put a 2" EMT conduit in and I could physically fit alot of #12 THHN conductors inside I would have to derate the #12 THHN to 80% of its ampacity when I reached 4-7 conductors. If this is not correct please advise. Thanks!

Work Gear for Electricians and the Trades
Re: # of conductors in conduit #74753
02/04/07 01:00 PM
02/04/07 01:00 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
You are correct, it doesn't matter what size conduit you use, the derating requirements start with 4 current carrying conductors

Roger

Re: # of conductors in conduit #74754
02/04/07 07:03 PM
02/04/07 07:03 PM
T
Tom H  Offline
Member
Joined: Jan 2005
Posts: 74
Milford, Ct, USA
Look in the code though, the normal use amperage and derateing amperage of some guages of wire are different. No code book here at home, but you derate from the higher amperage, still paying attenetion to the max amperage for that particular guage. If I remember correctly.

Code theory is so fun...

Re: # of conductors in conduit #74755
02/05/07 01:40 PM
02/05/07 01:40 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Are you talking small wires or large? For #12 THHN (90C), for instance, Table 310.16 allows 30A, but 240.4(D) restricts #12 to 20A maximum. For derating, though, you would use table 310.16, and would be able to put 7-9 #12 THHN conductors in a conduit before having to derate below 20A.

You do not have to count grounds for derating purposes, and may or may not have to count the neutral, depending what kind of circuit(s) you have. And I don't know if there is a code that explicely states it, but switched conductors (like in a 3-way switch) should only count as one conductor too, as only one will ever be considered a "conductor" at any given time.

Re: # of conductors in conduit #74756
02/05/07 02:07 PM
02/05/07 02:07 PM
S
SolarPowered  Offline
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
Also note that you can put up to 20 CCC's in one pipe if you use #10 for 20A, and #12 for 15A. That approach is used a good deal in commercial work.

Re: # of conductors in conduit #74757
02/05/07 05:24 PM
02/05/07 05:24 PM
S
stevecheyenne  Offline
Member
Joined: Nov 2006
Posts: 38
Yorba Linda, CA
Especially if you're upsizing the wire for voltage drop anyway.

Re: # of conductors in conduit #74758
02/05/07 07:50 PM
02/05/07 07:50 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
Are you still having misunderstandings with your same piece of 2" conduit and the same plant engineer?
Quote
switched conductors (like in a 3-way switch) should only count as one conductor too,


That would apply only to the travellers. The switchleg conductor must be counted as a current carrying conductor.

[

[This message has been edited by electure (edited 02-05-2007).]

Re: # of conductors in conduit #74759
02/05/07 08:13 PM
02/05/07 08:13 PM
K
kyelectric  Offline OP
Member
Joined: Aug 2005
Posts: 64
Electure, I explained to the plant engineer that the larger size conduit does not mean that I can fill it all the way up. He wants to use it for "future expansion" but I told him about the code making me derate the conductors after 4. Anyway, I did everything legally, they just ended up eating alot of wire cost because I had to upsize the #12's to #10's and the #10's to #8's. Thanks for the input!

Re: # of conductors in conduit #74760
02/05/07 08:16 PM
02/05/07 08:16 PM
K
kyelectric  Offline OP
Member
Joined: Aug 2005
Posts: 64
SolarPowered, what do you mean by CCC's? Something...Circuit Conductors. I need to know more about this. Thanks!

Re: # of conductors in conduit #74761
02/05/07 08:24 PM
02/05/07 08:24 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
CCC = current carrying conductor


Don(resqcapt19)
Page 1 of 8 1 2 3 4 5 6 7 8

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,378 Are you busy
187,310 Re: Forum
176,653 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.005s) Memory: 1.0323 MB (Peak: 1.2075 MB) Zlib enabled. Server Time: 2018-09-22 21:13:33 UTC