Halogen bulbs trip breaker. #74625 01/28/07 09:01 PM
Joined: Oct 2005
Posts: 10
R
redneck Offline OP
Member
Customer has complaint. He has recessed lights in the bathroom,and when the bulb blows,it trips the breaker. Bulbs are Halogen,120v,Sylvania double life,Capsylite Par 20.

Doesn't happen often,maybe a couple times a year. Breaker only trips when the bulb blows. Standard breaker,not GFCI,and lights are on separate circuit from Receps in Bath.

We didn't do the job,but he called me wondering what it could be.

Any ideas?????

Russell

Work Gear for Electricians and the Trades
Re: Halogen bulbs trip breaker. #74626 01/28/07 09:53 PM
Joined: Jun 2005
Posts: 821
S
ShockMe77 Offline
Member
If the circuit breaker is tripping it can only be one of three things: an overload, a short circuit, or a ground fault.

Re: Halogen bulbs trip breaker. #74627 01/28/07 09:57 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
Breaker trips also include physical shock, strong magnetic field, and over temperature.

I tend to doubt that any of these, are in fact the cause of this behavior.

Larry

Re: Halogen bulbs trip breaker. #74628 01/28/07 10:59 PM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
there is good chance when the filment break it will delope a arc current like HID for a split sec that just enough to trip the breaker

that one possiblty i can think of

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Halogen bulbs trip breaker. #74629 01/29/07 01:08 AM
Joined: Dec 2005
Posts: 860
R
RODALCO Offline
Member
Check the loading on the circuit concerned.
If say for example a 16 Amp beaker runs at 14 Amps lighting load, the cold inrush current from all the lamps and the arc from the lamp failing may be just enough to trip the braker.

Is it always the same lampfitting or all over the place ?


The product of rotation, excitation and flux produces electricty.
Re: Halogen bulbs trip breaker. #74630 01/29/07 09:45 AM
Joined: Feb 2002
Posts: 22
W
wageoghe Offline
Member
I have a fixture (outdoor floodlight) with halogen bulbs (stab in, not screw in) and it (apparently) tripped the breaker when one the bulbs blew. I noticed that other lights (inside the garage) on the same breaker were not on, so I reset the breaker and found that the only thing amiss, at least that I could tell, was the blown bulb in the floodlight.

Re: Halogen bulbs trip breaker. #74631 01/29/07 02:06 PM
Joined: Sep 2006
Posts: 26
B
Beachboy Offline
Member
I have two 90 watt PAR 40 halogen floodlight bulbs in an outdoor light fixture. Every time a bulb burns out, it trips the 15 amp breaker. I wrote General Elecric lighting department asking their opinions on this, and all they did was send me an apology and a case of new flood bulbs.

Re: Halogen bulbs trip breaker. #74632 01/29/07 03:39 PM
Joined: Jul 2004
Posts: 625
S
SolarPowered Offline
Member
I'm thinking a breaker rated "HACR" might be a good workaround, if that's not what's already there. They would be more likely to hold while the lamp filament clears, but will still adequately protect the wiring.

Re: Halogen bulbs trip breaker. #74633 01/29/07 05:27 PM
Joined: Jan 2006
Posts: 558
R
Rewired Offline
Member
I remember back in my school days every time an overhead projector would burn out a lamp it almost always would trip the breaker. The breakers were Sq-D and located right in the room so it was not too troublesome to reset actually.

A.D

Re: Halogen bulbs trip breaker. #74634 01/29/07 07:02 PM
Joined: Oct 2000
Posts: 2,721
Scott35 Offline
Broom Pusher and
Member
Marc hit the nail on the head!

Halogen Lamps have what is known as "The Halogen Cycle", which should be known for extended Lamp Life.

Simply put, to get the most life out of the Lamp, keep it as Horizontally Level as possible (+/- 4°).
This causes the Atomized Fillament to land back on the Filament, during operation.

When the Filament fails under load, the Atomized material allows an arc to be sustained, and the Arc has no Resistance (actually has negative resistance) - so there is a large increase in load current, which trips the breaker.

Same would occur if any Non-Ballasted Discharge Lamp was thrown across the line.

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,386 Are you busy
209,282 Re: Forum
196,579 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3