AE-Gifts, Affordable Everyday
0 members (), 1,096 guests, and 21 robots.
#7381 02/01/02 10:02 PM
Anyone here know if a manufacturer like Burndy or the like makes wire reducers, for reducing larger size wires at large breakers?. I somewhat remember using them years ago, but am not sure. This part of the latest project has 4 parallel runs of 3-750's, sized for the distance, terminating at a 1200 amp 3-pole. The breaker was sent with provisions for up to 4- 500's per pole. Its a Seimen's "Sentra" Breaker.I think I remember being able to get hyd. press on reducers with a solid end that would fit.Just not sure if they are available in that size.Any thoughts?
Regards,
NS4M
#7382 02/01/02 11:12 PM
[Linked Image from ecommerce.ilsco.com]
You must be talking about these. They are available from Ilsco and other manufacturers. This one (Ilsco) is available in 750MCM size with a 500MCM size pin. The offset variety, unfortunately, are available for aluminum only. www.ilsco.com/
[This message has been edited by Nick (edited 02-01-2002).]
#7383 02/02/02 12:10 AM
Thanks for the info, Nick.
cheers,
NS4M
#7384 02/02/02 12:25 AM
ahhhh a mack adapter...correct me if i am wrong.
#7385 02/02/02 07:06 AM
that's what i call em' [Linked Image]