#72670 - 12/06/06 10:51 PM Fault Current  
nwelectric  Offline
Junior Member
Joined: Jun 2005
Posts: 4
hiram, ga.
We have bid a condo project with a 600a single phase meter main on each bldg with 3 200a breakers feeding 3 condos per bldg and 1 100a breaker for a house panel. The meter main is spec to have a 600a MCB. The engineer says Isc at 37,191 at service with Isc 29,246 worst case at the apartment panels. I bid using Square D components in meter main at 44k aic. If I use mcb and each 200a at 44k aic shouldn't I be good to use 10K panels (again spec as MCB panels) in the units. I would have 44k and another 44k in series. What do you think???

NW


Frank

Work Gear for Electricians and the Trades

#72671 - 12/06/06 11:22 PM Re: Fault Current  
Dave T  Offline
Member
Joined: Jan 2005
Posts: 155
Waukesha, WI, USA
Are the OCPDs series rated?


#72672 - 12/06/06 11:43 PM Re: Fault Current  
nwelectric  Offline
Junior Member
Joined: Jun 2005
Posts: 4
hiram, ga.
Waiting on Sq D to answer that based on their bid for service.


Frank

#72673 - 12/07/06 12:39 AM Re: Fault Current  
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
nw
Can you give me an estimate of cost difference for the 2 options for breakers? Just curious.

[This message has been edited by Bob (edited 12-06-2006).]


#72674 - 12/07/06 04:11 AM Re: Fault Current  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Most of the breaker companies have that info for series rating on-line - but are often hard to find...


Mark Heller
"Well - I oughta....." -Jackie Gleason

#72675 - 12/07/06 11:31 AM Re: Fault Current  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Square D has a listing of their series ratings in their Digest (pages 2-8 and 2-9).

In general you can not apply three devices in series and still have a series rated system. You may have to change each apartment to a main lug only style.

Is this a single 600A main breaker and meter feeding seperately mounted breakers which then feed the individual apartments? Or, is it a 600A main feeding a meter center with individual combination meter sockets for each circuit (Square D type MP or EZM) which then feed each apartment?


#72676 - 12/07/06 01:20 PM Re: Fault Current  
Jps1006  Offline
Member
Joined: Jan 2004
Posts: 615
Northern IL
Quote
In general you can not apply three devices in series and still have a series rated system. You may have to change each apartment to a main lug only style.


Well that kind of defies common sense. If it's series rated with two, wouldn't more be better? Is there an electro-mechanical reason to this or is it just because it hasn't been tested this way for the listing?


#72677 - 12/07/06 02:19 PM Re: Fault Current  
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 854
Titirangi, Akld, New Zealand
Single Phase 600 Amps !!

Don't they share the load over three phases and bring 1Ø, 100 Amp services into the individual appartments ?


The product of rotation, excitation and flux produces electricty.

#72678 - 12/07/06 03:54 PM Re: Fault Current  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Quote
Well that kind of defies common sense. If it's series rated with two, wouldn't more be better? Is there an electro-mechanical reason to this or is it just because it hasn't been tested this way for the listing?


It all has to do with dynamic impedance of the devices opening as well as the static impedance of the circuit. Because of this devices must be tested in series.

Square D does have three tier ratings for use with their multi-metering devices.



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.8006 MB (Peak: 0.9660 MB) Zlib enabled. Server Time: 2017-08-17 21:33:13 UTC