0 members (), 164 guests, and 15 robots.
#72374 11/27/06 09:59 PM
I recently went on a service call for some high bays. While up in the lift I noticed the electric unit heaters had 277V nameplates but were installed in a building with 240V. No 277V is available.
(The motors are 277V rated as well)
The customer says they are about two years old?
Any thoughts as to potential problems?
Thanks
#72375 11/27/06 10:11 PM
Is there a chance that there are some Buck/Boost transformers somewhere?
We have done this before for this very situation.
Roger
#72376 11/27/06 10:19 PM
No Transformer Roger,
Small building, panel in sight of heaters.
I checked to see if there was one hiding.
Thanks
#72377 11/27/06 11:02 PM
You won't get you maximum power output for heating.
240 volts is 86 % of 277 volts.
By V²/R you only get 75% of your heating capacity.
For the motors it depends if they have to start a heavy load or not.
If it is only to drive a fan i can't see any problems with it.
#72378 11/27/06 11:31 PM
I doubt that you will have any problems but it wouldn't hurt to contact the mfg. to put your mind at ease.
Joe
#72379 11/28/06 01:42 AM
Only thing I can think of would be a conflict of something meant to run with a grounded phase vs. phase to phase... I'm not sure if this would be an issue in your case though...