I recently went on a service call for some high bays. While up in the lift I noticed the electric unit heaters had 277V nameplates but were installed in a building with 240V. No 277V is available.
(The motors are 277V rated as well)
The customer says they are about two years old?
Any thoughts as to potential problems?
Thanks
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Is there a chance that there are some Buck/Boost transformers somewhere?
We have done this before for this very situation.
Roger
|
|
|
|
Joined: Nov 2004
Posts: 53
OP
Member
|
No Transformer Roger,
Small building, panel in sight of heaters. I checked to see if there was one hiding.
Thanks
|
|
|
|
Joined: Dec 2005
Posts: 869 Likes: 4
Member
|
You won't get you maximum power output for heating. 240 volts is 86 % of 277 volts. By V²/R you only get 75% of your heating capacity.
For the motors it depends if they have to start a heavy load or not. If it is only to drive a fan i can't see any problems with it.
The product of rotation, excitation and flux produces electricty.
|
|
|
|
Joined: Nov 2005
Posts: 827 Likes: 1
Member
|
I doubt that you will have any problems but it wouldn't hurt to contact the mfg. to put your mind at ease. Joe
|
|
|
|
Joined: Feb 2004
Posts: 1,438
Member
|
Only thing I can think of would be a conflict of something meant to run with a grounded phase vs. phase to phase... I'm not sure if this would be an issue in your case though...
|
|
|