#72060 - 11/18/06 08:24 PM Stupid question time  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
You have 3 bathrooms in a house. No other equipment will come off of the 20 dedicated circuit. How many circuits for the bathrooms?


Work Gear for Electricians and the Trades

#72061 - 11/18/06 08:34 PM Re: Stupid question time  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
One if you want.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#72062 - 11/18/06 08:41 PM Re: Stupid question time  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
Now how many of us would only install 1?


#72063 - 11/18/06 08:51 PM Re: Stupid question time  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
For me it would depend on what the prints called for.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#72064 - 11/18/06 09:00 PM Re: Stupid question time  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
I was always taught that each bathroom was to have it's own circuit for the GFCI.


#72065 - 11/18/06 09:15 PM Re: Stupid question time  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I may have misled you.

You can either power everything in one bathroom from one 20 amp circuit or you can power just the receptacles in as many bathrooms as you want with one 20 amp circuit.

Check out 210.11(C)(2)


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#72066 - 11/18/06 09:35 PM Re: Stupid question time  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
I understand, i was just taught that each bathroom GFCI outlet has it's own circuit. This did not have anything else on it. So I would need 3 HR's for the bathrooms. Not including lights. Just outlet.


#72067 - 11/18/06 11:14 PM Re: Stupid question time  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
One dedicated 20 amp branch circuit to each bathroom is the better install, in my opinion. But it's only an opinion and a design issue. The Code allows for the (1) 20 amp circuit to be "jumped-out" to all the other bathroom as long as nothing else is on the circuit besides bathroom recpeptacles. The Code also allows for lighting to be included on this 20 amp circuit as long this circuit doesn't feed other bathrooms.


#72068 - 11/18/06 11:29 PM Re: Stupid question time  
mahlere  Offline
Member
Joined: Nov 2005
Posts: 507
New Jersey
simple, truthful answer - as many as the customer is willing to pay for.


#72069 - 11/18/06 11:37 PM Re: Stupid question time  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
I would say one circuit for all 3 baths.

If you want to be nice, 2 circuits. 1 in the master and the other feeding the other 2. one of those other 2 is most likely gonna be a 1/2 bath where the plug ussually is not used much.


Shake n Bake

Page 1 of 3 1 2 3

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.8168 MB (Peak: 0.9920 MB) Zlib enabled. Server Time: 2017-10-16 22:06:15 UTC