Circuit tester #71921
11/10/06 05:50 PM
11/10/06 05:50 PM
T
Taylor  Offline OP
Junior Member
Joined: Nov 2006
Posts: 2
Salem, Oregon, USA
Does anyone know how sensitive those little three prong circuit testers are? We were using them to confirm ground in the 110 outlets in our plant, but recently discovered that they can be misleading. One of them registered a gound ok but the ground measured 1700 ohms. We are now, of course, going around with a proper VOM rechecking all receptacles.

Work Gear for Electricians and the Trades
Re: Circuit tester #71922
11/10/06 07:44 PM
11/10/06 07:44 PM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
IMHO, I wouldn't use one of the cheapo ones for anything commercial at all.

Re: Circuit tester #71923
11/10/06 10:14 PM
11/10/06 10:14 PM
N
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Those testers use neon bulbs, which can light on a milliamp or less of current flow. They tell you only that there is some kind of path to ground, not that it is a GOOD path.

Re: Circuit tester #71924
11/13/06 05:52 PM
11/13/06 05:52 PM
T
Taylor  Offline OP
Junior Member
Joined: Nov 2006
Posts: 2
Salem, Oregon, USA
Thanks guys. We are no longer using these things in the plant. I never really thought much of them anyway, but we were sucked in by OSHA. There field agents use these same chepo gadgets to check for grounds during their investigations.

Re: Circuit tester #71925
11/13/06 07:39 PM
11/13/06 07:39 PM
R
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 856
Titirangi, Akld, New Zealand
In New Zealand we use the AVO-Megger LT 310 Loop Impedance Tester on the 230 volts MEN system.
The best way to test is to use a loop impedance tester instead of relying on neons which can give you false readings.
This one imposes a test current between the phase and neutral and earth.
It will tell you in Ohms and kiloAmps what fault level is available.
it will also confirm that the polarity is correct.


The product of rotation, excitation and flux produces electricty.
Re: Circuit tester #71926
11/13/06 08:01 PM
11/13/06 08:01 PM
S
scameron81  Offline
Member
Joined: Feb 2004
Posts: 75
Healdsburg, ca, USA
Check out this interesting link regarding OSHA and their cheapo testers.

http://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=INTERPRETATIONS&p_id=21410


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,143 Are you busy
185,607 Re: Forum
174,943 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.005s) Memory: 0.9753 MB (Peak: 1.1216 MB) Zlib enabled. Server Time: 2018-07-20 20:37:04 UTC