Can someone tell me what application an electrical interlock would have on a 200 amp elevator disconnect switch?

Horizontal Ad
Joined: Sep 2001
Posts: 806
N
Member
What do you mean by an "electrical interlock"?

A solenoid that prevents the switch from being thrown? That might prevent the power from being turned off when the elevator is between floors.

Joined: Feb 2004
Posts: 75
S
Member
The interlock is required for hydraulic elevators with automatic recall. When the power goes out the elevator automatically returns to the first floor and lets the passengers out. When working on the system and you turn off the disconnect for the sake of safety you don't want the elevetor moving down to the first floor. When the NC mechanical interlock opens it tells the elevator not to recall to the first floor even though the power is out. It has been a while since I have done an elevator but I am pretty sure thats the reason behind it.


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 34
Joined: June 2004
Top Posters(30 Days)
Popular Topics(Views)
558,408 Are you busy
432,716 Re: Forum
401,819 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5