Does anybody know of a simple wiring diagram for hooking up a two phase motor to a three phase supply?

We have an old mortising machine with a two phase 240 volt motor on it.

Replacing the motor is cost prohibitive, as it's cast into the machine.

It was working, and I can hook it up the way it was, it's just the way it was wasn't any where close to code.

I would like to cord connect it too.

Thanks

TW

Work Gear for Electricians and the Trades
Re: Two phase motors #71773
11/06/06 04:09 PM
11/06/06 04:09 PM
P
PEdoubleNIZZLE  Offline
Member
Joined: Jun 2004
Posts: 176
McKeesport, PA, USA
I think I have a diagram here somewhere, but I won't be able to post it until later tonight.

Re: Two phase motors #71774
11/06/06 05:02 PM
11/06/06 05:02 PM
J
jraef  Offline
Member
Joined: Jul 2004
Posts: 101
San francisco, CA, USA
Look up the diagram for a "scott tee" transformer connection. Here is one, http://www.lcmagnetics.com/scott.htm

Here is a thread from Mike Holt's on the subject which has another diagram inside. http://www.mikeholt.com/cgi-bin/codeforum/ultimatebb.cgi?ubb=get_topic;f=3;t=001104;p=


JRaef
Re: Two phase motors #71775
11/07/06 01:27 AM
11/07/06 01:27 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
There are a few ways of going at this, depending on what level of complexity you intend to apply.
i.e.:
* some complexity is OK,
* whatever we can do to run the Motor the best way possible, is the only approach we will take,
* basically having it run is OK,
* no one really knows how to address this one.

If the Motor is a 2Ø 3 Wire Motor, it might be something that could simply be directly connected to an appropriately rated (Voltage wise) 3Ø Power System, without the need of any "Phase Alteration" techniques.

If the Motor is a 2Ø 4 Wire type, &/or the Machine needs to be driven from an actual 2 Phase System, then choose one of the following Transformer Options described below:

[Linked Image]

Fig. 1: 3 Phase 3 Wire "Closed" Delta Primary to 2 Phase 4 Wire "Taylor" Secondary.

This arrangement would be classified "Higher Complexity", as there are 3 Transformers, and some "non-standard" tap points (86.6% taps).

It does offer the best stability and load balancing options, and is very much a "Steadier 2 Phase Output" from a 3 Phase Supply.

Actual Phase Offset - in degrees, may "Creep" around, resulting in something that might be 105 degrees in one case, 82 degrees in another, or set precicely at 90 degrees all the time.

I am not sure of any issues of how well this connection scheme performs, in regards to the two individual Phases being exactly at, or remaining steadilly at, 90 degree offset.
(btw, the "two individual Phases" are the separate 1 Phase 2 Wire "Sets", represented as "...'A' & 'B' ... Phase 1..." and "...'A' & 'B' ... Phase 2..."

[Linked Image]

Fig. 2: 3 Phase 3 Wire Open Delta "Tee" Primary to 2 Phase 4 Wire Open Delta "Tee" Secondary.

Here is a simpler approach to the issue, yet still involves a "non-standard" Transformer (the 86.6% tap again!).
The configuration is much simpler to install, but has some balancing issues, which lead to some level of instability.

It nonetheless is still a 2 Phase 4 Wire SDS, derived from a 3 Phase supply - and the degree of offset may be more "easier" to keep at 90 degrees in this arrangement.

Again, I am unaware of any issues regarding Phase offset in these 2 Phase configurations.

[Linked Image]

Fig. 2: 3 Phase 3 Wire Open Delta "Tee" Primary to 2 Phase 3 Wire Open Delta "Tee" Secondary.

This one is somewhat similar to the one shown above in "Figure 2" - only there is a "Common" Conductor derived from two coil ends, and results in a 3 Wire output.

Additional options may include Motor-Generator setups, VFDs with 2 Phase output design intentions, or a stand-alone Diesel Prime Mover driven Generator.

Something to mention:
Many low power polyphase dry-type transformers (upto 15 KVA), with a Secondary rated as 208Y/120V 3 Phase 4 Wire, are in fact an Open Delta Tee configuration.
This is only a mention, but something to ponder...

Many options available, others may have much better examples to choose from; your results may vary [Linked Image]

Scott35

*** REFERENCES ***

Links to 2 Phase pages at ECN:

2 Phase Transformer Schematics

Information relating to the posted images in this reply.

2 Phase Motor Drawings

Some Schematics of 2 Phase Motors.

S.E.T.

p.s.

Quote

It was working, and I can hook it up the way it was, it's just the way it was wasn't any where close to code.


Could you expand on this a bit, such as:

* How was it hooked up before,

* Was it connected to a 3 Phase system _DIRECTLY_ or _INDIRECTLY_,

* The Code Issues encountered on the existing installation.

TIA (Thanks In Advance)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Two phase motors #71776
11/07/06 10:21 AM
11/07/06 10:21 AM
T
Trainwire  Offline OP
Member
Joined: Mar 2002
Posts: 360
Strasburg,PA,USA
Sorry everyone, but I'm back.

I hope to get some pictures posted of this "installation" both before and after.

It was hooked up before by running cords from the machine to the panel box, protecting 12 gauge cord with 60 amp fuses. It was hooked to a three phase system, motor phase one, hooked to one and two, and motor phase two hooked to two and three. It worked, for the most part, sometimes it wouldn't start, and you had to turn it off and try again.

I found a diagram in the 1996 edition of Ugly's. I think that will work. From the looks of it it's how it was hooked up before. What I hope to do is cord connect it with a plug.

Scott I am emailing a pdf of the page in Ugly's, maybe you can post it.

The machine is rarely used. To go the transformer route is to spend waaay more money than the machine is worth. We can buy a second hand machine for less.
Thanks

I will be back as I have time.

TW


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
BigB 4
Popular Topics(Views)
249,474 Are you busy
187,390 Re: Forum
176,732 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9736 MB (Peak: 1.1128 MB) Zlib enabled. Server Time: 2018-09-26 08:44:10 UTC