R.V. Parks Calculations #69758
09/18/06 12:43 PM
09/18/06 12:43 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Looking at a R.V. park voltage drops on distances so great. Ideas???. 35 sites two 50 ampers then rest 30-20 amp aprox 100ft to ist then 80 ft between each & two rows.
Makes for some long runs
9600x2=19200 plus 3600 x 33=138000
138000 x 42%(table 551.73)=57960 divided by 240=241.5 amps.
for service calculations .
each row I take it also by 551.73

Pnl ---------------------------------------
----------------------------------------
around 1400 ft each row
additional rows i know would help.
lugs at most good fer 250mcm '
more rows possibly needed
anyone run into this before?

Yoopers

Work Gear for Electricians and the Trades
Re: R.V. Parks Calculations #69759
09/18/06 02:53 PM
09/18/06 02:53 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Can you move the main distribution to the center of the rows? That way you would have 4 shorter runs instead of 2 long runs.

Larry

Re: R.V. Parks Calculations #69760
09/18/06 03:55 PM
09/18/06 03:55 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
That is what they try to do in the parks here. They set transformers and maypole out to the lot runs. We found out the allowable calc is probably not going to be enough with these new land yachts.
They tend to use most of the 50a you give then when the AC is on


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,848 Are you busy
184,205 Re: Forum
173,446 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.9504 MB (Peak: 1.0740 MB) Zlib enabled. Server Time: 2018-05-21 03:24:00 UTC