Having a bad morning,what is the wire size for 50 amp generator. Told the H.O 6-3. Doesn't want to pay. He already has 8-3 ran from previous install of portable. Thanks
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
If it is 8/3 NM than it is rated 40 amps because of 334.80
If was 8/3 MC or 8 AWG in conduit it would be rated 50 amps.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2002
Posts: 125
OP
Member
|
It is 8-3 NM thats why I told him that.
|
|
|
|
Joined: Oct 2005
Posts: 100
Member
|
Even #6 AWG is STILL inadequate.
Conductors for standby generators need to be sized not less than 115% of the generators nameplate rating: NEC 445.13. In this case 50A x 115% = 57.5A, so you need to go with #4 AWG minimum in this application.
Joe
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Joe that is a good point.
However I believe Sparks gave us the breaker size which is not the same as the generators rating.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2002
Posts: 125
OP
Member
|
I forgot about the 115% rule. The genorator is rated at 50 amps. It's been awhile since iv'e installed one. It is going to be one of those Bryant all-in-one setup. The only proble is that where he wants it is about 40' away. And he wants to try to reuse what he has. Thanks again Sam