ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
334.80 and fire caulk
by gfretwell. 06/21/18 11:35 AM
Calling all Non-US members!! (Non-US only)
by HotLine1. 06/13/18 01:50 PM
GE Lighting Recalls LED Tube Lamps
by Admin. 06/12/18 09:32 PM
Ketra Recalls Recessed Downlights
by Admin. 06/12/18 09:17 PM
diazed fuses
by Texas_Ranger. 06/11/18 07:31 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 45 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Generator #69672
09/16/06 08:24 AM
09/16/06 08:24 AM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
Having a bad morning,what is the wire size for 50 amp generator. Told the H.O 6-3. Doesn't want to pay. He already has 8-3 ran from previous install of portable. Thanks

Work Gear for Electricians and the Trades
Re: Generator #69673
09/16/06 08:49 AM
09/16/06 08:49 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
If it is 8/3 NM than it is rated 40 amps because of 334.80

If was 8/3 MC or 8 AWG in conduit it would be rated 50 amps.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Generator #69674
09/16/06 09:13 AM
09/16/06 09:13 AM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
It is 8-3 NM thats why I told him that.

Re: Generator #69675
09/16/06 01:10 PM
09/16/06 01:10 PM
J
JJM  Offline
Member
Joined: Oct 2005
Posts: 100
Even #6 AWG is STILL inadequate.

Conductors for standby generators need to be sized not less than 115% of the generators nameplate rating: NEC 445.13. In this case 50A x 115% = 57.5A, so you need to go with #4 AWG minimum in this application.

Joe

Re: Generator #69676
09/16/06 01:22 PM
09/16/06 01:22 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Joe that is a good point.

However I believe Sparks gave us the breaker size which is not the same as the generators rating.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Generator #69677
09/16/06 03:35 PM
09/16/06 03:35 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
I forgot about the 115% rule. The genorator is rated at 50 amps. It's been awhile since iv'e installed one. It is going to be one of those Bryant all-in-one setup. The only proble is that where he wants it is about 40' away. And he wants to try to reuse what he has. Thanks again Sam

[This message has been edited by Sparks30 (edited 09-16-2006).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,236
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
twh 5
Admin 2
Popular Topics(Views)
247,671 Are you busy
184,991 Re: Forum
174,296 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.004s) Memory: 0.9745 MB (Peak: 1.1212 MB) Zlib enabled. Server Time: 2018-06-23 04:13:10 UTC