ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photos of the Week:

1923 Los Angeles Wireman's Handbook
1923 LA Wiremans Hbk

Random Gallery Image:
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 680 guests, and 21 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#69469 09/10/06 10:10 AM
Joined: Jun 2006
Posts: 34
CDS Offline OP
Member
Bidding on small welding shop 400 amp 1 ph
It is a metal butler building , already built on slab , sidewalk poured all the way around . Question is , I can tie ground to steel easily but with slab already poured , and sidewalk , I can't tie to rebar or use ground rods without cutting concrete . any advice would be appreciated .

Horizontal Ad
#69470 09/10/06 12:47 PM
Joined: Jul 2004
Posts: 10,015
Likes: 37
G
Member
I have seen them drill a hole in the concrete for a rod, just bear in mind it has to be 8' in the dirt so the rod needs to be longer than 8'. If you can find a place that is out of the traffic path that may be an option.


Greg Fretwell
#69471 09/10/06 10:29 PM
Joined: Sep 2006
Posts: 98
A
Member
With the sidewalk already poured does that mean that all the plumbing lines to the street are already roughed in? That would be a readymade route to use if the plumbing is not in. Otherwise, I would use a short length of rigid steel to cross the walk with a kick down on the outside end.

#69472 09/11/06 10:34 AM
Joined: Oct 2002
Posts: 482
Z
Member
I've done this by drilling, as gfretwell suggested. I drilled through the slab with a 7/8 bit (avoiding the 2' footer around the parameter of the building if at all possible) and then drove a 10' copper clad ground rod. If I recall, I even did this with a stainless rod ages ago for one application. Some heavy duty urethane caulk in and around the hole and rod and squeezed into the hole (after you blow it out) is a good touch to avoid water intrusion.

NOTE: Be VERY carefull not to drive the rod anywhere near a possible water or waste run. Carefull note where plumbing fixtures are in relation to your desired rod location BEFORE you even think about drilling and driving. Nobody wants to chip and dig to do a reapir on a sewer line =)

#69473 09/11/06 07:42 PM
Joined: Jun 2006
Posts: 34
CDS Offline OP
Member
Thanks for advice , as simple as it sounds , I never thought of drilling through the slab

#69474 09/12/06 07:34 PM
Joined: Jun 2005
Posts: 821
S
Member
Almost Fried...

now there's a memorable screen name!

#69475 09/15/06 11:25 PM
Joined: Jan 2005
Posts: 39
S
Member
I always drill through the foundation and pound in a 10' rod,I thought this was the common way everyone does it.Takes a couple seconds with a good rotorary hammer.

Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
Top Posters(30 Days)
Admin 3
Popular Topics(Views)
365,347 Are you busy
288,196 Re: Forum
266,895 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5