feeder protection #69129
08/29/06 06:09 AM
08/29/06 06:09 AM
C
carranoelectric  Offline OP
Junior Member
Joined: Aug 2006
Posts: 4
stratford ct
Is the secondary feeder from a 75 kva xfrm protected from the primary breaker? I have a 100 amp 480 v breaker on the primary with a 200 amp 208 v secodary to a panel. Do I need a 200 amp main or can I use main lug and have the 100 amp breaker protect the 200 amp feeder?

[This message has been edited by carranoelectric (edited 08-29-2006).]

Work Gear for Electricians and the Trades
Re: feeder protection #69130
08/29/06 06:27 AM
08/29/06 06:27 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
NEC 2002 240.21(C)(1) says you need a breaker on the secondary within a limited distance.


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,024 Are you busy
181,016 Re: Forum
171,265 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.9412 MB (Peak: 1.0586 MB) Zlib enabled. Server Time: 2018-02-20 02:02:16 UTC