0 members (), 413 guests, and 17 robots.
#69129 08/29/06 07:09 AM
Is the secondary feeder from a 75 kva xfrm protected from the primary breaker? I have a 100 amp 480 v breaker on the primary with a 200 amp 208 v secodary to a panel. Do I need a 200 amp main or can I use main lug and have the 100 amp breaker protect the 200 amp feeder?
[This message has been edited by carranoelectric (edited 08-29-2006).]
#69130 08/29/06 07:27 AM
Ron Offline
NEC 2002 240.21(C)(1) says you need a breaker on the secondary within a limited distance.
Ron