0 members (), 748 guests, and 11 robots.
#69070 08/26/06 01:36 PM
ehill Offline OP
Interesting report...
http://www.copper.org/applications/electrical/building/pdf/bundle_evaluation_report.pdf
I've been wondering about this recently.
Eric
[This message has been edited by ehill (edited 08-26-2006).]
#69071 08/26/06 01:53 PM
Wow. I never knew that using a butt load of smaller holes, like do was actually a better wiring method. I always thought that I was just too cheep to buy a larger drill bit.
#69072 08/26/06 02:12 PM
That's darn interesting. I have to admit, having never personally witnessed the adverse effects of bundling Romex, and having seen it ignored by almost every local "authority" in residential electrical construction, I was darn skeptical about what threat bunlding posed.
Obviously, the bundling does have a serious impact on heat generation.
However, I would have liked the study to address several things: What was the average temperature rise for a single cable carrying the same load as identical bundled cables?
And speaking from personal experience I can say that in a lot of resi. construction cables are regularly bundled for distances far in excess of 24". They may not be packed together in a hole and fire-stopped, so their is certainly more heat dissipation, but by how much? What happens when that same bundle is covered with ten inches of blow-in fiberglass?
I think I'll be a lot more cautious about how I route cables now after seeing this.
-John
#69073 08/26/06 03:00 PM
ehill Offline OP
I question their test method, though... To have the bundle pass through the top plate, and then back down the top plate? That's not a "real-world" situation. (Maybe I'm missing something.)
Seems like with all they went through in their test scenario, they could have simulated the "real world" a little better.
Still, the report is interesting.
Eric
#69074 08/26/06 03:04 PM
ehill Offline OP
You know, John, I think there's a lot of factors involved, too... I mean... South facing walls without shade in Las Vegas are going to get a lot hotter than a north facing wall in colder places of the county.
OT, a little, we sometimes balk at local code, but I think that's exactly why local codes should exist. Local needs might be complete overkill for other parts of the country.
Eric
#69075 08/26/06 03:13 PM
I am not as concerned by the routing of the cables in the test but the loading is IMO unrealistic in dwelling units.
in combination with 73% loading of all the cables
I find it extremely unlikely you would find a bundle of NMs (6) in a dwelling all loaded to 73% or any combination that averages out to 73% at the same time.
How would that happen in any modern dwelling construction?
Even the simultaneous 60% loading of six two wire circuits in a dwelling unit seems remote to me.
#69076 08/26/06 03:18 PM
e57 Offline
Used to be that inspectors here required only one cable per hole, but in the last few years they realized that this turned the framing into swiss cheese, and now allow two only. (Allowing two 12/2/2's) In the guiese of not exceeding 9 current carrying, as you would in conduit, same for stacker and other bundles. Taking a large bundle of cables, like some would above a panel into a single connector isnt allowed for these same reasons.
That said, if I go a few cities over, where bundling is ignored, you can tell the difference. You really can feel the difference in warmth in the bundles. And on occassion see a slight discoloration of romex sheathes in stuff installed around ten years ago.
#69077 08/26/06 03:32 PM
e57 Offline
Any building with base-board heat, or AC...
#69078 08/26/06 04:23 PM
Both of those examples are non-continuous loads.
If you had the six circuits all supplying electric heat circuits it would be unusual for all six circuits to have each of their zones all needing heat at the same time.
I take, as I am sure you do many current readings.
It is unusual for many circuits to be at 60% load in a dwelling unit.
Proof of this is the fact you may have 500 amps worth of breakers in a 200 amp panel.
Anything is possible but we regularly assume certain loading characteristics, most of Article 220 is based on assumptions.
#69079 08/26/06 04:25 PM
And besides all that.
It's the copper org bringing us the message, more copper less heat. [Linked Image]