0 members (), 1,224 guests, and 17 robots.
#68803 08/16/06 08:39 PM
Peter Offline OP
I was hooking up an Ansul system today with a shunt trip breaker. I connected the shunt trip to the normally closed contacts from the Ansul system. It seems that every time I turn on the breaker for the Ansul system, both of the pizza oven breakers trip. Should I attach to the normally open contacts?
Should I wire the two pizza ovens in parallel or series?
~Peter
#68804 08/16/06 09:55 PM
around here, once the Ansul ring is pulled,
EVERYTHING electrical on
the cooking line must be de-energized,
the gas valve must close ,
the MUA for the hood is shut down,
and the hood exhaust fans shall continue to run....
is the Ansul system cocked ? it sounds like it is tripped and needs to be reset.
unwire the ansul switch and reset the shunt breaker , that should tell you
pizza ovens in parallel or series???
#68805 08/16/06 11:22 PM
Peter Offline OP
The Ansul system is cocked.
What I mean by series/paeallel is there are two, three pole breakers, each with its' own shunt trip mechanism [takes up on breaker space]. I wired these in series instead of parallel.
What I need to know is what trips the shunt trip? Is it the presence of voltage or the absence?
~Peter
#68806 08/17/06 06:14 AM
The shunt trips work upon applied voltage.
You will need to wire two breakers in parallel.
One side of the shunt coils will wire to a neutral or neutral bar, (this is assuming 120 v shunt trip units) the other sides get the voltage through the Ansul switch. You will feed the Ansul common with 120 v and wire your switch leg to the open switch conductor when the Ansul system is cocked.
Roger
[This message has been edited by Roger (edited 08-17-2006).]
#68807 08/17/06 08:56 PM
Just an aside: For anyone who needs it, I came up with a way to interconnect the intake and exhaust fans to the control box using only 3 wires.
There are two advantages: (1) freeing up the second micro-switch for use with shunt-trips or other purposes; (2) being able to use simpler wiring methods (MC, etc. as required).
It can easily interface with existing wiring. Of course, anything other than 120v motors will need relays/contactors to use this method.
Before:
[Linked Image from fineelectricco.com]
After:
Larry Fine
Fine Electric Co.
fineelectricco.com
#68808 08/18/06 11:20 AM
X
Normally Open
#68809 08/18/06 09:47 PM
Peter Offline OP
Today I changed from serial to parallel. This seems to make sense. I had already changed from the N.C. contacts to the N.O. contacts.
Thank you for your adviCe.
~Peter