ground testing #68350
08/03/06 02:56 PM
08/03/06 02:56 PM
J
jay8  Offline OP
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
What is a ground resistivity test, and how does one go about testing a system ground?

Work Gear for Electricians and the Trades
Re: ground testing #68351
08/03/06 04:20 PM
08/03/06 04:20 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa


Greg Fretwell
Re: ground testing #68352
08/03/06 04:23 PM
08/03/06 04:23 PM
H
hypress  Offline
Member
Joined: Jul 2004
Posts: 129
Charleston WV
The most common way to test ground resistance is with a fall of potential tester some times called a earth megger.
It has 3 leads one goes to the ground rod under test,the second lead goes to a driven test electrode 60'from the rod under test and the 3rd driven test electrode is at 120'from the rod under test.All three of the points should be in a streight line. Now what happens is that a voltage is passed between the rod under test and the rod at 120'. The rod at 60' measures the voltage drop between the 60'point and the rod under test.The unit works on null balance an you adjust the 4 knobs until the zero center meter reads zero.The figure at the 12:00 on the knobs is the resistance of the ground.
A word of caution a new ground rod will have a higher resistance than one that has been in the ground for a couple of days.Let the earth heal around the rod before testing you will get a better reading.

Re: ground testing #68353
08/03/06 05:39 PM
08/03/06 05:39 PM
L
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Service Upgrade $2000
Ground Testing $800

Be done with it, install the two rods!

Re: ground testing #68354
08/03/06 06:29 PM
08/03/06 06:29 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Along with Gfretwells link here is another one to check out.
http://www.tradeport.on.ca/ApplicationNotes/aemc.pdf

If this isn't a performance test required for a job specification, I would do as LK sugests and drive the second rod.

Roger

Re: ground testing #68355
08/03/06 07:02 PM
08/03/06 07:02 PM
L
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Here in Jersey the public, and commercial pools, need a performance test, and inspection, there are companies that are set up for just that work.

Re: ground testing #68356
08/03/06 07:22 PM
08/03/06 07:22 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
That's funny. I think the best electrode in the world is probably a gunite pool. You just can't call it that.

I have worked on several projects where they did performance testing of the grounding system. Mostly radio tower/equipment shelter installations and toll booths. The radio engineers design the tower systems and we had Bert Lavin (former CMP kinda guy)working on the tool booths. They turn out to be a lightning magnet around here.


Greg Fretwell
Re: ground testing #68357
08/04/06 07:04 AM
08/04/06 07:04 AM
Z
Zog  Offline
Member
Joined: Sep 2005
Posts: 120
Charlotte, NC
To add to hypress description the center lead (Potential lead) should be placed at a distance that is 52% of the distance of the furthest lead (Current lead), record the value and move the center rod to 62%, record, then 72%, record. These values should be plotted to show a relativly flat line to verify your readings. If the plot is not flat your readings are being affected by the sphere of infulence of the ground rod under test and the current lead and the current lead should be moved further away from the rod under test and the entire procedure repeated until your 3 point plot is relativly flat.

Another method that is becoming more accepted is the clamp on method, simple and fast, but the test equipment is more expensive.


MV/HV Testing Specialist, "BKRMAN"
Re: ground testing #68358
08/04/06 11:19 AM
08/04/06 11:19 AM
J
jay8  Offline OP
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
thanks for the feedback so far, FYI this is a commercial building, concrete encased grounding grid I believe, since the structure sits on a pier. Also 12.4kv coming in, with 4 2500kva transformers in the room.

Re: ground testing #68359
08/04/06 11:31 AM
08/04/06 11:31 AM
Z
Zog  Offline
Member
Joined: Sep 2005
Posts: 120
Charlotte, NC
You want to see less than 5 ohms for that type of system per NETA MTS


MV/HV Testing Specialist, "BKRMAN"

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,050
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,211 Are you busy
189,192 Re: Forum
178,873 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 14 (0.004s) Memory: 1.0098 MB (Peak: 1.1856 MB) Zlib enabled. Server Time: 2018-12-15 14:06:05 UTC