Calculating neutral loads. #68022
07/27/06 05:22 PM
07/27/06 05:22 PM
T
Trick440  Offline OP
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Whats the formula to find the amps a neutral is carrying?

And if 220 doesn't need a nuetral to work,.. is there current on the nuetral?

So I need some schooling an nuetrals. Any and all help is appreciated. [Linked Image]


Shake n Bake
Work Gear for Electricians and the Trades
Re: Calculating neutral loads. #68023
07/27/06 09:15 PM
07/27/06 09:15 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Trick,
Quote
Whats the formula to find the amps a neutral is carrying?
are you asking about three phase or single phase?

Quote
And if 220 doesn't need a neutral to work,.. is there current on the nuetral?
Since a neutral is not needed in this voltage (not true of all world voltage systems)source, it doesn't exist to have current flowing on it.

Roger

Re: Calculating neutral loads. #68024
07/27/06 09:55 PM
07/27/06 09:55 PM
T
Trick440  Offline OP
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Single phase.

Three phase wouldn't hurt either.


Shake n Bake
Re: Calculating neutral loads. #68025
07/28/06 07:14 AM
07/28/06 07:14 AM
D
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
For a wye system the nuetral current is calculated by:

N= Sq root of (A^+B^+C^)-(AB+AC+CB)

^=squared

For split phase(single phase) the nuetral current is calculated by:

A-B or B-A.

Does this make sense?

Re: Calculating neutral loads. #68026
07/28/06 02:37 PM
07/28/06 02:37 PM
T
Trick440  Offline OP
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
nope it don't make sense.

The Wye formula I see and understand.. except for, What is A, and B?

The single phase. Same situation, what is the A and B refering to. Volts, Watts, amps?

And with this slash (-) are you tring to say A, minus B?


Shake n Bake
Re: Calculating neutral loads. #68027
07/28/06 03:55 PM
07/28/06 03:55 PM
D
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Trick, the A,B,C are the currents in phase A, Phase B, and Phase C.

So for a split(single)phase service, the nuetral current is the unbalnced current flowing between phase A and phase B.

So if 30 amps were flowing on phase A, and 15 amps were flowing on Phase B, the nuetral current would be: Yes it is a minus...

A-B=N
30-15=15

On a wye service, if we had 150amps on A, 110amps on B, and 75amps on C.

N= Sq root of (A^+B^+C^)-(AB+AC+CB)
N=Sq root of (150^+110^+75^)-((150*110)+(150*75)+(75*110)
N=Sq root of
(22500+12100+5625)-((16500)+(11250)+(8250))
N=Sq root of
(40225)-(36000)
N=Sq root of
(4225)
N=65 amps


How does that look?



[This message has been edited by Dnkldorf (edited 07-28-2006).]

Re: Calculating neutral loads. #68028
07/28/06 05:13 PM
07/28/06 05:13 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Trick, to go along with Dnk's posts here are some graphics for help in visualizing the single phase neutral

BTW, I like to refer to the ends of single phase windings as legs, not phases.

So with this said, A and B in Dnk's post would relate to legs 1 and 2

[Linked Image]

[Linked Image]

[Linked Image]

Roger

[This message has been edited by Roger (edited 07-28-2006).]

Re: Calculating neutral loads. #68029
07/30/06 04:55 PM
07/30/06 04:55 PM
T
Trick440  Offline OP
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Thats great guys. I see now. Thank you. [Linked Image]


Shake n Bake
Re: Calculating neutral loads. #68030
07/30/06 05:44 PM
07/30/06 05:44 PM
D
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Anytime.......

Re: Calculating neutral loads. #68031
07/30/06 08:12 PM
07/30/06 08:12 PM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 787
Oradell NJ USA
All the above assumes that all loads are pure resistors, like incandescent light bulbs. If we talk about a computer server farm fed by 3 phase 120V, things get more complicated. Computer power supplies draw large spikes of current at the very peak of voltage of the phase they are connected to. When the voltage on phase A peaks, computers on phase A draw their spikes of current and return them to the neutral. Later, 120 degrees of the 60Hz cycle, phase B peaks, and computers on phase B draw their current spikes, and return them to the neutral. Likewise, 120 degrees later for phase C. No overlap of these current spikes (in terms of time). Spikes last about 5% of the cycle time. Note that the neutral will see 3 times as much spike current than any one phase (assuming equal phase loading). Thus you'd need a thicker wire for the neutral.

[This message has been edited by wa2ise (edited 07-30-2006).]

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,160 Are you busy
185,635 Re: Forum
174,999 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.006s) Memory: 1.0249 MB (Peak: 1.2013 MB) Zlib enabled. Server Time: 2018-07-22 16:29:22 UTC