205
17
I had a home inspector list a number of items wrong on one of my clients houses that is for sale. One item was to change the receptacle in the toilet room to a GFCI. This room only has a toilet. I told him he was wrong. The definition of a bathroom includes a sink. I installed the GFCI anyway, but I believe he was wrong. He also said the oven (rated at 240v/8500 watts) was over-fused. It had a double-pole 40 breaker. I didn't change it, but quoted sect.210-19(A)(3). Was I wrong?
Posts: 5,485 Likes: 4
On the GFCI issue, you are correct. No sink, it's not a bathroom. But, GFCI's are cheap, so no harm done. As for the oven, "overfusing" would depend upon the size of the wire feeding it. Assuming #8 or larger, I don't see a problem there, either.
You're not the first to have had issues with HI's. You might be diplomatic, and ask the bozo to check out some HI web sites, for some "clarification."
Question, cause I don't know...
If this toilet room, is located inside a room that has a sink, then I would think this does require GFCI protection.
The sink doesn't have to be inside the same room as the toilet does it?
A room within a room, is what I am trying to explain..
Posts: 10,042 Likes: 37
A room within a room is another room. If you have to open the door to wash your hands after using the toilet the toilet room is not a bathroom.
But a bathroom is defined as an "area", not a single room..
is he the realtors inspector or the authority having jurisdiction.
Peter; this is the realtor's "home inspector"...definately the AHJ.
Dnk; this is a room with a door off the sink room...kind of like a closet off a bedroom...perhaps this brings up the AFI in a bedroom closet discussion
Reno; the cable was 6/3 SER alum. And to be diplomatic, I'd call him "Mr. Bozo"!
HLC, I believe he was right then, this should be a bathroom.
IMO
[This message has been edited by Dnkldorf (edited 06-28-2006).]
Posts: 2,518 Likes: 1
That's a water closet I guess.
However, the big question would be: why does anyone need an outlet there anyway??? A ceiling light or wall sconce should be well enough.
Maybe he was looking at the toilet room from the aspect of a guy on a three day bender stumbling in to relieve himself, loosing aim and ZAP! Stranger things have happened.
