200 Amp Panel With 4..... #64557
04/10/06 06:08 PM
04/10/06 06:08 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
My home panel has a main breaker 200 amp, but it is 4 breakers (4 x 200 amp)with at tie bar....shouldn't it just be a 2 pole?

Work Gear for Electricians and the Trades
Re: 200 Amp Panel With 4..... #64558
04/10/06 06:16 PM
04/10/06 06:16 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
What you have is very likely a GE panel.

The breakers are actually four single pole 100 amp breakers rigged with an internal common trip mechanism and set up in such a way that two 100s are paralleled on each phase giving a total ampacity of 200 amps per phase.

I have this very panel in my own house.

[This message has been edited by iwire (edited 04-10-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 200 Amp Panel With 4..... #64559
04/10/06 06:34 PM
04/10/06 06:34 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Yes they are GE.

Why does GE do this versus using 2 of 200 amp breakers?

Re: 200 Amp Panel With 4..... #64560
04/10/06 06:39 PM
04/10/06 06:39 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I can only imagine it is cheaper.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 200 Amp Panel With 4..... #64561
04/10/06 07:48 PM
04/10/06 07:48 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
The first manufacture I remember doing this was ITE (Siemens). GE and Square D (Homeline) must have liked the idea since they started doing the same thing.

curt


Curt Swartz
Re: 200 Amp Panel With 4..... #64562
04/10/06 07:50 PM
04/10/06 07:50 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Seimens used to do it also. Circa 1990.

Re: 200 Amp Panel With 4..... #64563
04/10/06 09:15 PM
04/10/06 09:15 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
If you look at max sum of breaker stab, it may be below 200A. Many of the stab ons are rated at 145-165 max sum of each stab, due to either the reduced contact area of that type of breaker, or the way the buss-work is cut and bent, might reduce cross-section.

GE has a really small contact area on stab breakers.
Murray/Siemens have reduced cross-section.
Older CH, and SqD QO just dont have either to make higher amperage CBs work out without burning the busswork.
Newer CH have bigger greased pads for contact on the stab in CBs in the 50 to 200 range.

Our PM just found out the hard way about this very issue, trying to get a 320/400 MM w/ 200A and another 200 out of the 200 distribution portion of a 20/40 in the same panel. (165A Max sum per stab)

FYI If you need CBs for feeders in the 100 -200 range you may be better off with bolt on's.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: 200 Amp Panel With 4..... #64564
04/10/06 11:39 PM
04/10/06 11:39 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Some tears back, an engineer explained to me that the 4-section GE main breaker is comprised of two currect-sensing sections (like a 2-pole, 200a breaker) and two parallel contact-only sections (sort of like fully-rated auxillary contacts) for lower overall contact resistance.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: 200 Amp Panel With 4..... #64565
04/11/06 04:49 AM
04/11/06 04:49 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Larry I bet he was guessing. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,380 Are you busy
187,991 Re: Forum
177,541 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.003s) Memory: 1.0015 MB (Peak: 1.1690 MB) Zlib enabled. Server Time: 2018-10-18 09:26:55 UTC