0 members (),
148
guests, and
25
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2004
Posts: 78
OP
Member
|
Does anyone know of a Square D type circuit breaker that is a side by side?....basically letting you put 2 of 15 amp breakers where usually only 1 is placed. Are they called a particular name?
|
|
|
|
Joined: Mar 2004
Posts: 814
Member
|
Homeline or QO? New Homeline twins are available. As far as QO, I've seen some old twins that are side by side rather than stacked, don't know if they are still made. Maybe someone else will chime in.
|
|
|
|
Joined: Nov 2005
Posts: 507
Member
|
they make QO tandems as well. I don't know if they are available in canada or not.
|
|
|
|
Joined: Aug 2005
Posts: 265
Member
|
Yes, the QO tandems are available in Canada.
Sixer
"Will it be cheaper if I drill the holes for you?"
|
|
|
|
Joined: Jul 2004
Posts: 625
Member
|
QO tandems can be had in both Class CTL and non-Class CTL versions. They aren't side-by-side, though--they're in a tandem arrangement.
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
I saw a tandem 14 sq-d in a bolt on panel in a resturant the other day. I was a bit suprised. I have never seen tandems in a bolt on before. Is this common? Or did somebody jury rig here. I didn't remove the panel cover, as I was there to look at something else.
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
Square D Panelboards accept both QOB (bolt on) and QO (plug on) breakers. I have been told that they recommend using QO breakers instead of QOB when adding additional breakers in the field. I can pretty much guarantee that the panelboard was not listed for tandem breakers and I’m sure the breaker used was clearly marked non-CTL for replacement use only.
BigB, what new Homline tandem breakers are you referring to? HOMT breakers in 15 and 20 amp have been available since the beginning of Homeline. They later added the larger quad breakers (30-50).
Curt
Curt Swartz
|
|
|
|
Joined: Jan 2005
Posts: 316
Member
|
Here in the US - Home depot does carry qo tandum breakers that are the side by side set up. They two different types for both QO panels and CH. I'm not sure about Canada though.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
|
|
|
|
Joined: Jul 2001
Posts: 599
Member
|
The old Square D tandem breakers were front-to-back. The tandems since the 80's have been side-by-side. The new design gives the 2 pole devices the appearance of a quad breaker, but it is really (1) 2pole + (2) 1poles.
All UL Listed panels built since the 60's are CTL. So non-CTL breakers should only be installed in panels that are over 40 years old that have wiring diagrams showing which spaces are designed for tandem circuits.
My personal belief is that non-CTL tandem breakers should go the way of the old delta breakers.
|
|
|
Posts: 440
Joined: December 2001
|
|
|
|
|