Shockme77, #12 and a 20 amp breaker would be fine unless there is a considerable distance involved, then a #10 may need to be considered.
The 80% load on the OCPD would only come to play if you were talking about more than 16 amps for longer than 179.99 minutes at a time. (continuous)
Roger