I have a ongoing thing with my boss about bonding, we are doing a 450ft run of 4/0 and #2 ground. Going though 4 j-box's. There are no concentic k.o's all are punched, I say we should use bonding bushings not just locknuts for the bond. He says just plastic bushings. Who would be right. Thanks Sam
( This is a panel off the main gear )
[This message has been edited by Sparks30 (edited 03-04-2006).]
While bonding bushings would not be a bad idea you don't need them. You only need them if using concentric or ecentric knockouts. Read 250.92 and 250.97
Jesus may have been a capenter,but God was an electrician.Genesis1:3
2005 NEC 250.92 is for services . As this is a feeder . (250.97) deals with Bonding over 250 volts to ground. If this was a 120/240 or 120/208 volt. Bonding bushings on a feeder would not be required Even if concentric or ecentric was involved. IF they were in good condition.