#62619 02/22/06 09:07 AM
Joined: Feb 2006
Posts: 1
S
Junior Member
I am currently working on a remodel on a residential property with multiple buildings. The main house was built pre-1906 with tube and knob system (2 hot and neutral). The building I am working on is a cottage located about 100 feet away from the main house where its electricity originates. The house's main panel has 4 double pole breakers, each feeding a sub-panel.
On the service are the three cables as expected. The three lines that feed the cottage travel through a plastic conduit up the side of the building, across to opposite end on the house and up to a gooseneck and back down another plastic conduit into the ground then ground where it travels under a swimming pool over to the sub-panel in the cottage. At the gooseneck there is an additional cable (green insulated which must be a ground).
The owners have been having problems with the electrical for some time and I have found numerous issues with the wiring and made those changes. I have replaced the sub-panel with a newer model. The 4 that enter the building are connected to appropriate spots, (the two hot cables to a 100 Amp circuit breaker, neutral to the neutral bus and the last to the ground bus. The neutral is un-bonded.
When tested the 2-poles test correctly but I also have 120 across the neutral and ground. I decided to add another grounding rod at the cottage to be sure that the sub-panel is in fact grounded but still have the same test results and when I use a plug tester on the receptacles I all three lights light up.
Any suggestions?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#62620 02/22/06 09:19 AM
Joined: Oct 2001
Posts: 172
W
Member
If you feel like you are over your head here you probably are. If you are a contractor, why haven't you called an electrician? You don't really want the liability on this one do you?

#62621 02/22/06 10:01 AM
Joined: Apr 2004
Posts: 349
Member
Ditto Watthead.
Quote
but I also have 120 across the neutral and ground.
This can lead to a disaster, and right now, your name is on the liability list, even though you didn't cause the initial problem. You should call an electrician asap.

Radar


There are 10 types of people. Those who know binary, and those who don't.
#62622 02/22/06 10:27 AM
Joined: May 2002
Posts: 1,716
R
Member
To add to Wattheads and Radars posts, a ground rod will have no effect on your problem, you need to get an electrician involved.

Roger