Re: Service Entrance Splice
#62313
02/16/06 10:13 AM
|
Joined: Aug 2004
Posts: 69
Member
|
I just do a quick continuity check with a fluke meter. Lately I have been using the ILSCO IPC KUP-L-TAP it is a self piercing tap that does not require any stripping of the wire. I was a little hesitant at first because it does not seem like it would make an adequate connection vs stripping the wire and a split bolt. But I have not had any short term problems with them little pricey though about 15 each
|
|
|
Re: Service Entrance Splice
#62314
02/16/06 11:07 AM
|
Joined: Sep 2001
Posts: 806
Member
|
I use the Kup-L-Taps as well. The higher price is worth it to me for not having to play around with stripping the live drop and taping an energized split bolt while working off a ladder. The things are reusable, so I do try to get them back from the utility when they come out to make their permanent connections. I use a standard split bolt on the neutral to save a few $.
Have experienced no reliability problems with them at all, even on a couple installations where the PoCo never replaced them.
I ALWAYS check the wiring for shorts/grounds with a meter before making up the service drop splices.
|
|
|
Re: Service Entrance Splice
#62315
02/16/06 11:53 AM
|
Joined: Aug 2004
Posts: 69
Member
|
As far as a know in central NJ PSE&G does not come back to redo the splice so what we do is perminate. I usally will also tape the taps friction and plastic since they do not get removed. Maybe the tape is overkill, I dont know but I do it anyway.
|
|
|
Re: Service Entrance Splice
#62316
02/16/06 04:15 PM
|
Joined: Oct 2004
Posts: 39
Member
|
Here in central Maine the power comany is the ONLY one that connects to their lines. You can't even pull the meter unless there is a IMEDIATE danger. If a electrician tapped or retapped the SE cable to the power company lines I'm pretty sure the penality would death by hanging!
Thats how we do it up in the woods!
|
|
|
Re: Service Entrance Splice
#62317
02/16/06 04:40 PM
|
Joined: Aug 2004
Posts: 69
Member
|
I wish Frank I would love it I hate tyeing in live it is so nice when you get a new construction job and the poco does the tie in when they bring there drop in from the pole
|
|
|
Re: Service Entrance Splice
#62318
02/16/06 04:40 PM
|
Joined: Feb 2006
Posts: 5
Junior Member
|
We do it all the time here in Chicagoland and ComEd very rarely comes to re-connect it. I personaly like Hi-pressing the wires myself and then rubber taping them just to be safe. Never with the meter in though.
|
|
|
Re: Service Entrance Splice
#62319
02/16/06 09:55 PM
|
Joined: Apr 2005
Posts: 116
Member
|
I use a megohmmeter on any type of feeder, before I energize it. It only takes a couple of minutes.
|
|
|
Re: Service Entrance Splice
#62320
02/16/06 10:02 PM
|
Joined: Jun 2003
Posts: 1,143
Member
|
I've used bugs (split bolts), the "butt connector" splices that you tighten with an allen wrench and the insulation piercing version. Tap Test? ![[Linked Image]](https://www.electrical-contractor.net/ubb/eek.gif)
|
|
|
|
|