#62269 - 02/12/06 01:37 PM grounding electrode conductors  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
when derating sevice conductors 4/0 for 3/0 copper for a 200 amp service do you use #2 for the grounding electrode conductor or #4.

[This message has been edited by lite bulb (edited 02-12-2006).]


Work Gear for Electricians and the Trades

#62270 - 02/12/06 06:04 PM Re: grounding electrode conductors  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,142
Estero,Fl,usa
There is no relief in 250.66 for derated service conductors. If it is 4/0 copper you need the #2

[This message has been edited by gfretwell (edited 02-12-2006).]


Greg Fretwell


Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7441 MB (Peak: 0.8629 MB) Zlib enabled. Server Time: 2017-12-14 04:22:12 UTC