grounding electrode conductors #62269
02/12/06 02:37 PM
02/12/06 02:37 PM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
when derating sevice conductors 4/0 for 3/0 copper for a 200 amp service do you use #2 for the grounding electrode conductor or #4.

[This message has been edited by lite bulb (edited 02-12-2006).]

Work Gear for Electricians and the Trades
Re: grounding electrode conductors #62270
02/12/06 07:04 PM
02/12/06 07:04 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,251
Estero,Fl,usa
There is no relief in 250.66 for derated service conductors. If it is 4/0 copper you need the #2

[This message has been edited by gfretwell (edited 02-12-2006).]


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,506 Are you busy
186,202 Re: Forum
175,667 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.004s) Memory: 0.9424 MB (Peak: 1.0562 MB) Zlib enabled. Server Time: 2018-08-14 15:33:31 UTC