ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Inspection camera help
by Bill Addiss. 09/19/18 10:50 PM
220/230/240V 60Hz Systems
by gfretwell. 09/16/18 12:37 PM
Acronis Backup 2017
by gfretwell. 09/16/18 12:46 AM
Tingle off the water spigot
by Trumpy. 09/15/18 03:24 AM
Lighting Load questions
by HotLine1. 09/14/18 07:04 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 44 guests, and 25 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
nm cable #621
02/14/01 06:34 PM
02/14/01 06:34 PM
S
sam  Offline OP
Member
Joined: Jan 2001
Posts: 29
when is it not okay to use romex cable? refering to the number of people that are to be using the building ? is it 100 persons.

Work Gear for Electricians and the Trades
Re: nm cable #622
02/14/01 07:52 PM
02/14/01 07:52 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,902
NY, USA
Sam,

If you have a code book see Article 336-5 Uses not permitted (for starters) and it lists a number of things. I'm not a good typer and it would take awhile to type out all of them - maybe someone else has it on Cd and can paste it here.

Bill

Re: nm cable #623
02/14/01 10:01 PM
02/14/01 10:01 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
sam;
check the handbooks expert text in "places of assembly"

Re: nm cable #624
02/20/01 01:42 PM
02/20/01 01:42 PM
D
dturner  Offline
Member
Joined: Feb 2001
Posts: 18
Harrisburg PA USA
336-4. Uses Permitted
Type NM, Type NMC, and Type NMS cables shall be permitted to be used in the following:
1. One- and two-family dwellings
2. Multifamily dwellings and other structures, except as prohibited in Section 336-5
3. Cable trays, where the cables are identified for the use
FPN: See Section 310-10 for temperature limitation of conductors.
(a) Type NM. Type NM cable shall be permitted for both exposed and concealed work in normally dry locations. It shall be permissible to install or fish Type NM cable in air voids in masonry block or tile walls where such walls are not exposed or subject to excessive moisture or dampness.
(b) Type NMC. Type NMC cable shall be permitted as follows:
1. For both exposed and concealed work in dry, moist, damp, or corrosive locations
2. In outside and inside walls of masonry block or tile
3. In a shallow chase in masonry, concrete, or adobe protected against nails or screws by a steel plate at least 1/16-in. (1.59-mm) thick, and covered with plaster, adobe, or similar finish
(c) Type NMS. Type NMS cable shall be permitted for both exposed and concealed work in normally dry locations. It shall be permissible to install or fish Type NMS cable in air voids in masonry block or tile walls where such walls are not exposed or subject to excessive moisture or dampness. Type NMS cable shall be used as permitted in Article 780.
336-5. Uses Not Permitted
(a) Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be used in the following:
1. In any multifamily dwelling or other structure exceeding three floors above grade
For the purpose of this article, the first floor of a building shall be that floor that has 50 percent or more of the exterior wall surface area level with or above finished grade. One additional level that is the first level and not designed for human habitation and used only for vehicle parking, storage, or similar use shall be permitted.
2. As service-entrance cable
3. In commercial garages having hazardous (classified) locations as provided in Section 511-3
4. In theaters and similar locations, except as provided in Article 518, Places of Assembly
5. In motion picture studios
6. In storage battery rooms
7. In hoistways
8. Embedded in poured cement, concrete, or aggregate
9. In any hazardous (classified) location, except as permitted by Sections 501-4(b), Exception, 502-4(b), Exception, and 504-20
(b) Types NM and NMS. Types NM and NMS cable shall not be installed in the following:
1. Where exposed to corrosive fumes or vapors
2. Where embedded in masonry, concrete, adobe, fill, or plaster
3. In a shallow chase in masonry, concrete, or adobe and covered with plaster, adobe, or similar finish


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,149
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 9
Popular Topics(Views)
249,304 Are you busy
187,237 Re: Forum
176,605 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.9600 MB (Peak: 1.0910 MB) Zlib enabled. Server Time: 2018-09-20 10:45:41 UTC