ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
by gfretwell. 03/20/18 12:06 AM
Recall notice: Southwire wi-fi wall switches
by sparkyinak. 03/15/18 06:03 PM
Goodman Manufacturing Recalls Modular Blowers
by Admin. 03/13/18 10:40 PM
MAAX Spas Recalls Hot Tubs and Swim Spas
by Admin. 03/13/18 10:29 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 31 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Old work- recessed light big problemo #61710
02/01/06 12:21 PM
02/01/06 12:21 PM
Haligan  Offline OP
Joined: Feb 2004
Posts: 111
Berkeley, CA USA
Existing old ceiling surface light to be replaced with recessed can. I take down the light and look in the box and discover it's a MAJOR junction box. There's no fill violation, but it's right at the limit with two difference circuits branching off in there. The junction boxes attached to the cans are completely undersized for this. I think this is a 'no-go'.

editorial note:
I'm ashamed to admit it, but I'm pretty much a bookworm electrician. I do a lot better work than some lifers I've seen, but because I've had very little time with a master sparky I'm sure I do a lot of things the hard way. Not having the benefit of years of experience. Now that California has mandated the licensing, my time is up. I have no where near the required apprentice hours necessary for the test.

Work Gear for Electricians and the Trades
Re: Old work- recessed light big problemo #61711
02/01/06 02:58 PM
02/01/06 02:58 PM
Radar  Offline
Joined: Apr 2004
Posts: 349
Los Angeles, CA
Licensing issues aside for the moment. First thing we need to know is if the space above the ceiling is accessable (attic?). Then we can work on a solution.

There are 10 types of people. Those who know binary, and those who don't.
Re: Old work- recessed light big problemo #61712
02/01/06 04:05 PM
02/01/06 04:05 PM
Steve Miller  Offline
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
Around here they consider the space above a recessed can as accessible (assuming you can get to it by removing the trim only). If it's an IC can you may be out of luck. We split up the jbox into 2 ... and charge accordingly [Linked Image]

Re: Old work- recessed light big problemo #61713
02/01/06 04:08 PM
02/01/06 04:08 PM
Trick440  Offline
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Just shove em all in there, it'll work. Even if you gotta leave the door off... whos gonna see it anyways....

lol... just kidding. Use a j-box if its attic accessible.

Shake n Bake
Re: Old work- recessed light big problemo #61714
02/01/06 04:44 PM
02/01/06 04:44 PM
Jim M  Offline
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
Besides the number of wires in the box, you will probably have an issue with the insulation rating of the existing conductors. Most recessed require 90 degree C wiring.

Although it would not be easy to find should something go wrong, perhaps a deep 1900 box to enclose the existing wires. This would be accessible thru the hole for the recessed.

Re: Old work- recessed light big problemo #61715
02/01/06 05:58 PM
02/01/06 05:58 PM
Haligan  Offline OP
Joined: Feb 2004
Posts: 111
Berkeley, CA USA
The location is a stairway landing in between floors. There is a good 11 inches of depth there. No insulation. I'll check the NEC tonight to see if a remodel can opening is accessible. If you can only get one arm through the hole is that accessible?

Installing a j-box through that opening is going to be a little proctological.

Re: Old work- recessed light big problemo #61716
02/01/06 07:04 PM
02/01/06 07:04 PM
Active 1  Offline
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
Besides the J-box in the can hole idea you have another option. Put a finish blank on the cieling box, Cut the can near by, and wip off the box to the can. If the blank is painted the same as the cielinf it does not look that bad.


Re: Old work- recessed light big problemo #61717
02/01/06 11:29 PM
02/01/06 11:29 PM
HLCbuild  Offline
Joined: Dec 2004
Posts: 209
Herndon,Va USA
I'll probably take some heat for this, but...if you are using a remodel type fixture, then the j-box of the fixture is accessed only by removing the recessed fixture. So I don't see a problem if you put another j-box in the ceiling accessible thru the same hole. However, I did see a UL listing once on Lightolier recessed fixtures that said if the hole was not at least 6" in diameter, it would not be listed for "feed-thru" wiring; i.e. you couldn't use that hole for the large j-box if the recessed light is less than 6". The 1100 series takes a 6 5/8" hole. (And Lightolier 1000 series, 5", and 2000 series, 3 3/4", are labeled suitable for feed-thru wiring, but they're not unless there is access from above!)


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,416 Are you busy
181,531 Re: Forum
171,579 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.005s) Memory: 0.9936 MB (Peak: 1.1509 MB) Zlib enabled. Server Time: 2018-03-20 09:25:06 UTC