What exactly is required when mixing voltages, ie. 208 & 277 in the same J-Boxes and conduits.
As far as labeling, color codes etc.
I know what is preferable, but what is required by code.
Thanks in Advance.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Jan 2005
Posts: 5,480
Likes: 3
Cat Servant
Member
They need to be separated by a non-conductive barrier.

Joined: Jan 2003
Posts: 4,391
I
Moderator
No barrier is required unless two devices in the same box have more than 300 volts between them.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Dec 2000
Posts: 4,294
Member
.....And at least one of those devices is a snap switch

Joined: Nov 2005
Posts: 826
Likes: 1
J
Member
Don't all of the conductors have to have an insulation rating appropriate for the highest voltage used?
Joe

Joined: Dec 2000
Posts: 4,294
Member
Yes, they do.
All of the Building Wire that I'm accustomed to working with has insulation rated at 600V, so it would qualify for highground's original query.

Now my question:
What is the insulation rating of Cat5/Cat6 etc. cable?
How about Bell Wire/Thermostat Wire?

Joined: Oct 2004
Posts: 806
Member
Quote
Now my question:
What is the insulation rating of Cat5/Cat6 etc. cable?
How about Bell Wire/Thermostat Wire?

Most CAT5/6 I've seen is rated at 300 volts. I'll check back on the new CAT6 I just used on a job, it's in the warehouse...

I've seen t-stat wire at both 150v and 300 volts. Not sure about bell wire.

Anyone? Anyone? Bueller? Bueller? [Linked Image]


Stupid should be painful.
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Nov 2000
Posts: 2,148
R
Member
Quote
What exactly is required when mixing voltages, ie. 208 & 277 in the same J-Boxes and conduits.
As far as labeling, color codes etc
See 210.5 in the 2005 NEC.
Don

the code section should be 210.5(C)

[This message has been edited by resqcapt19 (edited 01-19-2006).]


Don(resqcapt19)
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
What is the insulation rating of Cat5/Cat6 etc. cable?
How about Bell Wire/Thermostat Wire?
Then you have to look at 725.55(A). Even if the communications and controls cables have a voltage rating higher than that of the power conductors, you still can't mix them in the same raceway.
Don


Don(resqcapt19)
Joined: Jan 2005
Posts: 74
T
Member
725.55(D) allows for mixing voltage class wires so long as the class 2 wires pertain to a device in that box. A nice one for lighting control systems.