0 members (), 1,390 guests, and 9 robots.
Helicon Offline OP
What can be the reason for final inspection to fail? I wasn't there, but inspector called the homeowner and said something about Circuit-Breakers and hung up. the job was 2 bedrooms and the stairs.
both bedrooms' receptacles on same circuit: 20 AMPS, 12 AWG, 10 duplexes, also from this circuit is a light for outside.
Second circuit: 15 amps, 3 closet lights, 3 (50 W bulbs) recessed lights on stairs + 1 lamp, 1 light in bedroom, and in another bedroom chandelier with 5 bulbs, and 1 more light on the wall near the stairs(together 11 standard bulbs, and 3 recessed)
smokes (4) are from bedroom circuit.
3 phones.
This was kinda remodeling job, because when the guys was rebuilding upstairs he threw out old wiring, just left 2 cables that came from the panel.
Hmmm. I'll guess first.
My guess is that the wrong circuit breakers were installed.
The first person to ask is the inspector.
Just a shot in the dark but did you use ark fault breakers? Or did you use mini breakers that are not permited in your area?
[This message has been edited by Active 1 (edited 01-16-2006).]
Judging by what you posted my guess would be wrong breakers, either wrong type,size,or lack of arc fault. Ask the inspector and post it .
Helicon Offline OP
the breakers were already there, i didn't install them, i beilieve they are Squere D and a Squere D panel, the panel and the breakers were the only new things in that house when i first came.
+1 with Tom.
Call the building department & speak with the inspector.
Dave
Probably because its not an arc fault breaker and/or not the correct breaker.
Shake n Bake
Maybe smokes not on a dedicated circuit?
Helicon Offline OP
Everything's fine now,It was because there weren't Arc-Fault breakers.
YA! Ark faults.
Did I win a prize?