Electronic Ballast #60916
01/13/06 04:46 PM
01/13/06 04:46 PM
W
Wireless  Offline OP
Member
Joined: Jun 2005
Posts: 73
Los Angeles CA USA
Hi everyone. I have been having some problem with some 2x4 troffers. Customer called last week a bunch of fixtures are out I changed 6 of the ballasts. a few days later they tell me the breaker keeps tripping so I put my amp meter on it it was pulling 24a so I split the circuits instead of 2 circuits now there are 4 for all the lights. I come this morning I see 2 ballasts are out one is one I just changed. What am i looking for?

Work Gear for Electricians and the Trades
Re: Electronic Ballast #60917
01/13/06 05:00 PM
01/13/06 05:00 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Need more information to really help..how many fixtures were on each circuit, is the panel serving them 3 phase, were the circuits sharing a neutral?

Shared neutrals are a big no-no with ballasts, especially electronic ones. Harmonic currents add up rapidly and cause no end of problems and repeated ballast failures.

And any loose connections can kill e-ballasts rapidly. Had one case personally where we went through 3 ballasts on the same fixture until I pulled on the whip and the loose wirenut fell off in ther j-box. Fixed that and no more failures since (about 6 years now.)


Stupid should be painful.
Re: Electronic Ballast #60918
01/13/06 05:29 PM
01/13/06 05:29 PM
W
Wireless  Offline OP
Member
Joined: Jun 2005
Posts: 73
Los Angeles CA USA
about 20 lights per circuit. single phase service. lights are fed from a 3 wire circuit.

Re: Electronic Ballast #60919
01/13/06 05:40 PM
01/13/06 05:40 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
That shared neutral is doing twice the work of either of the ungrounded conductors. IMO you need to install a dedicated circuit and split up the fluorescent lighting.

Good luck!

Re: Electronic Ballast #60920
01/13/06 07:06 PM
01/13/06 07:06 PM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 785
Oradell NJ USA
Quote
single phase service

That shared neutral is doing twice the work of either of the ungrounded conductors.


If it's single phase (pair of 120Vs 180 degrees out of phase) electronic ballasts on both sides should be drawing their spikes of current at the same time (in respect to the timing of a 60 cycle waveform) and thus the neutral should be sharing/splitting the spikes the same way it would if the loads were just resistors. When you get neutral overload is when you have multiple phases, 120 degrees out of phase. Then the loads on phase A draw their spikes of current at a different time then those of phase B.

A bad connection on a neutral could cause problems like those you normally see with neutrals serving other kinds of loads.

[This message has been edited by wa2ise (edited 01-13-2006).]

Re: Electronic Ballast #60921
01/13/06 07:54 PM
01/13/06 07:54 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
20 ballasts per circuit? check the amount of current each is pullin, it can add up. As long as they are not on the same phase, the neutral in the 3wire circuit should only have the imbalance on it, if they are on the same phase, the current in the neutral will be the sum of the current on both phases.

Re: Electronic Ballast #60922
01/13/06 10:51 PM
01/13/06 10:51 PM
waymag  Offline
Member
Joined: Jan 2002
Posts: 67
dallas, texas, USA
Are the right lamps being used. Maybe too high a wattage for the ballast.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,552 Are you busy
180,359 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9846 MB (Peak: 1.1340 MB) Zlib enabled. Server Time: 2018-01-19 21:34:44 UTC