#60902 - 01/12/06 10:26 PM 3wire 3 phase grounded service  
sandsnow  Offline
Member
Joined: Sep 2004
Posts: 167
Irvine, CA, USA
Well finally ran into something interesting at work. not the same old MC and PVC.
This vintage 1960's service is supplied by POCO at 240V 3phase 3wire corner delta. And from a pad mount XFMR!! I always thought those went back to pole tops.
Anyway, the contractor has Sq D service equipment. I think it's a QED type, this is by phone call. According to Sq D bulletin QED boards are listed for use on corner grounded systems.
Has anyone hooked one of these up recently or at all???
I'm curious about the bonding provisions for the grounded phase.
Are they right there just as in a 4 wire board???
Is there an extra part or kit you need to order.
I want to be able to tell this guy some good info.
I am going to look at it tomorrow.
Thanks guys

--------------------
Larry LeVoir
Inspector
City of Irvine,CA


Larry LeVoir
Inspector
City of Irvine, CA

Work Gear for Electricians and the Trades

#60903 - 01/13/06 05:55 AM Re: 3wire 3 phase grounded service  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Larry,

Can't say that I have dealt with one of these systems lately (within the last 2-3 years), but between the mid 1980's and Y2K (year 2000), I dealt with a few here and there.
The more "Common" System in the "Old School Days" I ran across, was the Ungrounded 3 Wire Delta.

I have some Schematics + data in the Technical Reference section, which may be of assistance to you + the E.C.

Check out the Corner Grounded 3Ø 3 Wire Delta Topic for some assistance regarding the Corner Grounded Delta setup.

Scott35
https://www.electrical-contractor.net/ubb/Forum15/HTML/000078.html
(same as link text above)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#60904 - 01/13/06 07:55 AM Re: 3wire 3 phase grounded service  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
In Irvine? [Linked Image]

Amazing


#60905 - 01/13/06 10:43 AM Re: 3wire 3 phase grounded service  
sandsnow  Offline
Member
Joined: Sep 2004
Posts: 167
Irvine, CA, USA
Scott35
Great stuff on the diagrams. I don't know what I'm going to find when I go there. They will be useful to explain the system to the electrician. I hope the existing premises wiring was done correctly.

Scott(electure)
Yeah, Who would of thought in super clean Irvine

Here's a link to what I found on Sq-D's site. http://ecatalog.squared.com/techlib/docdetail.cfm?oid=09008926800b38e9

Interesting reading. It has a little on why they were used, code references, UL standard references, advantages and disadvantages.


Larry LeVoir
Inspector
City of Irvine, CA

#60906 - 01/13/06 11:35 AM Re: 3wire 3 phase grounded service  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,105
Estero,Fl,usa
I have seen it a couple times for pumping stations. A quick glance might have you thinking this was regular single phase. You are right about the equipment tho. Everything must be 3p rated and for the applied voltage.
The grounded conductor, a phase, is still white and you have your EGC green or bare. You can have all 2 pole breakers as long as they are 3p rated. Other than the equipment listing issues it is not that confusing. Just remember there is no downsizing of the "neutral" (one of the few times when that term is inappropriate for a grounded conductor) [Linked Image]


Greg Fretwell

#60907 - 01/13/06 11:55 AM Re: 3wire 3 phase grounded service  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
Everything must be 3p rated and for the applied voltage.

Some standard single phase equipment is listed for use on corner grounded delta systems. There is no need for overcurrent protection in the grounded phase. Also, many forget that the rules in Article 200 apply to the grounded conductor in this system.
Don


Don(resqcapt19)

#60908 - 01/13/06 01:32 PM Re: 3wire 3 phase grounded service  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Does the equipment need to be specifically rated for 3 phase service? Or is it sufficient that the equipment be rated for the voltage to ground?

As an analogous question: is a common 240/120 single phase residential panel suitable for use when supplied from two legs plus the neutral of a 208Y/120 supply? Or does it need to be labeled for that application?

-Jon


#60909 - 01/13/06 05:13 PM Re: 3wire 3 phase grounded service  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,105
Estero,Fl,usa
240.85 Applications.
...A two-pole circuit breaker shall not be used for protecting a 3-phase, corner-grounded delta circuit unless the circuit breaker is marked 1–3 <phase> to indicate such suitability.

[This message has been edited by gfretwell (edited 01-13-2006).]


Greg Fretwell

#60910 - 01/13/06 05:26 PM Re: 3wire 3 phase grounded service  
sandsnow  Offline
Member
Joined: Sep 2004
Posts: 167
Irvine, CA, USA
The sw/board turned out to be labled for 3phase 3wire, but no had provisions for bonding B phase. It appeared to have been ordered incorrectly. Sq-D's bulletin on this(see above post) specifically mentions to specify grounded B phase when ordering.
I was also dismayed to see a glaring violation of 408.3(A)(2) on Sq-D's part. Equipment ground buss located at the top mere inches away from unguarded service buss bars.
The contractor is trying to convince POCO to supply as ungrounded delta. I don't know if POCO is allowed to do this or will do it. If so, that will solve one problem.


Larry LeVoir
Inspector
City of Irvine, CA


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109