ark fault #60623
01/07/06 12:15 PM
01/07/06 12:15 PM
V
vlad_tepish  Offline OP
Member
Joined: Oct 2005
Posts: 39
Delavan,Wis,USA
looking for info on ark fault breakers,,,two bedrooms fed with 14-3 ,they share the neut ,when I use my testor everything checks out fine ,put a load on eather room the ark fault breaker trips,,,help???


Patrick
Work Gear for Electricians and the Trades
Re: ark fault #60624
01/07/06 12:31 PM
01/07/06 12:31 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
Arc faults also provide GFP protection (30ma GFCI). Some are even GFCI (5ma). In either case you won't be able to share neutral current. This is another reason why we should be able to put the "device" style nearer the point of use than the 2005 code allows. If you could install it in the first outlet after the "split" of the multiwire it would protect the bedroom.


Greg Fretwell
Re: ark fault #60625
01/07/06 01:51 PM
01/07/06 01:51 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Cuttler Hammer makes a good two indivdual circuit AFCI breaker made for 3-wire.

However Vlad it sounds like you have problems circuit or the load. Troubleshooting these can be a real PITA! Contact between another neutral or ground can do that. Most often it would trip right away, but have seen some that remain on until load is applied. Isolate the circuit and check to see if any continuity between the neutral and any other ground or neutral.

Load issues could be anything... Vaccuum cleaner with electronic speed controls, LCD screens, flouresant lighting, dimmers, etc. Many manufacturers have known equipment conflicts that just wont work with the breaker at all.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: ark fault #60626
01/07/06 03:46 PM
01/07/06 03:46 PM
HCE727  Offline
Member
Joined: Nov 2005
Posts: 186
Delaware County, PA, USA
I usually run a 14/2/2 if I am running 2 circuits for afci"s. I would like to check out that breaker, from Cutler Hammer.


Hank
Re: ark fault #60627
01/07/06 04:20 PM
01/07/06 04:20 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
http://www.eatonelectrical.com/unsecure/cms1/TB00500002E.PDF

page 27 BR215AF


[This message has been edited by e57 (edited 01-07-2006).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: ark fault #60628
01/07/06 04:30 PM
01/07/06 04:30 PM
togol  Offline
Member
Joined: Sep 2005
Posts: 421
NW In. USA
I thought Wis. deleted the AFCI requirement for 2005? why not just change them out for "normal" breakers


Tom
Re: ark fault #60629
01/16/06 09:52 PM
01/16/06 09:52 PM
V
vlad_tepish  Offline OP
Member
Joined: Oct 2005
Posts: 39
Delavan,Wis,USA
replaced the 2 single breakers with a double arkfault ,,everything is fine...thanks


Patrick

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,406 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.005s) Memory: 0.9842 MB (Peak: 1.1381 MB) Zlib enabled. Server Time: 2018-01-23 13:47:34 UTC