Electricians revenge
1 members (Scott35), 183 guests, and 10 robots.
#60614 01/07/06 11:02 PM
Gosh, if you aren't allowed to install 20 amp receptacles, how do you wire for a 20 amp AC with a 20 amp cord end?
I'd ask the inspection division to quote the code or local ordinance to you. Perhaps it is just folklore
#60615 01/07/06 11:47 PM
The 80% on #14, 12 and 10 wire is handled by 240.4(D).
#60616 01/08/06 11:52 AM
V
more info,,all the kitchen ,dinning room outlets are fed for 20 amp, with 15 amp recepticals.the ac is fed from the pannel to the outside disconect ,no need for a seperate outlet. the bath gfci's are all fed for 20 amp with 15 amp recepticals the rest of the house is all 15 amp unless there is an upgrade on somthing "like a wirlpool or a 220 outlet in the laundry or somthing like that.
Patrick
#60617 01/08/06 03:44 PM
My suspicion is that the AHJ is trying to make sure a full 20 amp load isn't plugged into a single outlet, i.e. 80% maximum loading allowed on a 20 amp outlet is 16 amps (unless all components are rated to operate at 100%).
That is not exactly what the NEC requires.
First lets think about a circuit with only one single 20 amp receptacle outlet connected to it.
That single 20 amp receptacle could be loaded 100%, the breaker feeding that receptacle could be loaded 100% for up to 3 hours or forever if it was 100% rated.
Now lets think of a circuit with two or more 20 amp receptacle outlets connected to it.
In this circuit we could plug in two or more items that total 20 amps and that 20 amps of load could again run 3 hours or forever with a 100% rated breaker.
The only time 80% comes into play is here.
210.21(B)(2) Total Cord-and-Plug-Connected Load. Where connected to a branch circuit supplying two or more receptacles or outlets, a receptacle shall not supply a total cord-and-plug-connected load in excess of the maximum specified in Table 210.21(B)(2).
So in a circuit with multiple outlets the total load can exceed 80% of the circuit rating but not at one particular receptacle.