grounding #6000
12/19/01 06:37 PM
12/19/01 06:37 PM
F
flush  Offline OP
Member
Joined: Dec 2001
Posts: 12
nj
i have a 3 phase 480/277 panel i wanted to bond to the building steel. which metal roof rafters that support the roof. is it ok to drill and 1/4x20 a lug or ive heard of a lug that the head of the bolt snaps off at the right torqe? which one would be legal

Work Gear for Electricians and the Trades
Re: grounding #6001
12/19/01 09:21 PM
12/19/01 09:21 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Are you bonding the Building Steel to the Electrical system via a connection at the Sub Panel, or are you planning to ground the Sub Panel by bonding it to the grounded Building Steel?

If Bonding the Steel to the Grounded Electrical System, then do so via approved lugs and bolt sizes according to the lug. Torque all to the specifications only ONCE!!! Do not re-torque the lug.
If the bolt used to land the lug snaps off when torqued, find a better bolt! [Linked Image]
Maybe someone can suggest what to do here. I have broke bolts during torquing, but they were few and far between [and sometimes the "Cheap'os" from the Home Depot's open bins].

Lugs have been known to strip out during torquing. Can't really elaborate much on this one except that "Doo-Doo Occurs" [Linked Image]

Now, if you are planning to ground bond a panel by connecting it to a grounded Steel frame, this would be something that falls under 250-32.
Could you expand a little more on your topic?

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: grounding #6002
12/19/01 09:39 PM
12/19/01 09:39 PM
A
aphares  Offline
Member
Joined: Dec 2001
Posts: 37
Indiana
2002 NEC, 250.53(C) Shall be connected in a manner specified in 250.70.
(exothermic welding,listed lugs,listed pressure connectors,listed clamps,or other listed means,Connections depending on solder shall not be used.
If the lug is listed for the wire property on the connection to the steal, than it can be connected to the building by the 1/4*20 screw, locknuted and torqed to the bolts manufacture standards. as long as any paint or primer is removed from the building steal first.
To insure a good connection than it would be recommended to install a min. (hex head bolt). and torqued.
A illegal connection would be with a self drilling screw...
As far as the other lug, again, as long as it is listed... (You are using for the purpose it is intended for.)

Re: grounding #6003
12/20/01 08:39 AM
12/20/01 08:39 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Yes there are torque indicating bolts and adapters that are designed to "twist-off" at the correct torque. These negate the need for a torque wrench.

Check out Ilsco and Burndy, I believe they both have adapters that go between a normal wrench and a socket. For dual headed twist-off bolts try Fastenal.

Re: grounding #6004
12/20/01 12:31 PM
12/20/01 12:31 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
aphares,
Quote
A illegal connection would be with a self drilling screw...

Is a self drilling screw always sheet metal screw? There are self-drilling, self taping machine screws that would be permitted for grounding connections.
Don(resqcapt19)


Don(resqcapt19)
Re: grounding #6005
12/20/01 07:06 PM
12/20/01 07:06 PM
A
aphares  Offline
Member
Joined: Dec 2001
Posts: 37
Indiana
My interpatation:
A sheet metal screw has threads that tear the metal than set their self by force. A self tapping screw would tap the threads in to the metal and could be screwed to a specific toque. The tapping screw would be legal. You are correct.....

Re: grounding #6006
12/20/01 07:36 PM
12/20/01 07:36 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Most enclosures that may be used where an EGC is installed will have a termination point such as one with a lug, or "a means provided" and this may be a simple "hump with a thread" to be used with a machine screws, and not a sheet metal screw.

Any kind of a "sheet metal screw" is not permitted.


[This message has been edited by Joe Tedesco (edited 12-24-2001).]


Joe Tedesco, NEC Consultant
Re: grounding #6007
12/20/01 08:41 PM
12/20/01 08:41 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Joe,
What is the definition of a "sheet maetal screw" and where do we find it. I know that the intent is to provide a secure electrical connection, but when you look in a hardware catalog you will find that the ones in your pictures are not shown as "sheet metal screws". Look at: http://www.mcmaster.com/param/asp/psearch.asp?FAM=selfdrill&desc=Self%2DDrilling+Screws

Here are "sheet metal screws": http://www.mcmaster.com/param/asp/psearch.asp?FAM=selfdrill&desc=Self%2DDrilling+Screws

I would not like to see either one of the above used to terminate an EGC, but if I was an inspector, I would have no grounds to turn down the self drilling screws. The code needs to be changed to require the use of a machine screw or a machine bolt to make the section clear and enforceable.
Don(resqcapt19)


Don(resqcapt19)
Re: grounding #6008
12/20/01 09:09 PM
12/20/01 09:09 PM
A
aphares  Offline
Member
Joined: Dec 2001
Posts: 37
Indiana
My picture of a self drilling screw.
It looks very much so like a mach. bolt, but the bottom of the bolt does not drill. A pilot hole must first be drilled,(smaller than the bolt) then the mach bolt is inserted into the hole when at the same time it acts like a tap. The bottom looks like a tap, but only about 1/2" up. The threads it makes will accept any normal mach. bolt of the same thread.

[This message has been edited by aphares (edited 12-20-2001).]

Re: grounding #6009
12/21/01 06:25 PM
12/21/01 06:25 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
....

[This message has been edited by Joe Tedesco (edited 12-24-2001).]


Joe Tedesco, NEC Consultant
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
dsk 2
Popular Topics(Views)
251,505 Are you busy
188,681 Re: Forum
178,384 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 1.0284 MB (Peak: 1.2055 MB) Zlib enabled. Server Time: 2018-11-16 09:54:35 UTC