suggested wire size #59696
12/12/05 11:03 PM
12/12/05 11:03 PM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
I'm installing a 1.5 hp 230V 11 amp single phase fan motor from a 120/208V panel about 250 feet away. Any suggestions for wire size.

Work Gear for Electricians and the Trades
Re: suggested wire size #59697
12/12/05 11:37 PM
12/12/05 11:37 PM
B
bot540  Offline
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
YOU'LL NEED TO PULL NO. 8 WIRE


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Re: suggested wire size #59698
12/13/05 12:08 AM
12/13/05 12:08 AM
G
George  Offline
Member
Joined: Feb 2002
Posts: 375
maybe only #10.

Re: suggested wire size #59699
12/13/05 12:31 AM
12/13/05 12:31 AM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
JK
Have you tried to do the VD caculations yourself?

Re: suggested wire size #59700
12/13/05 01:50 AM
12/13/05 01:50 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
10 drops 6.6v, 12 drops 10.6v @ 11a


Greg Fretwell
Re: suggested wire size #59701
12/13/05 06:53 AM
12/13/05 06:53 AM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
Bob,

I apologize, I have not. I was hoping someone would have previous experience with this.

Joe

Re: suggested wire size #59702
12/13/05 08:02 AM
12/13/05 08:02 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Not all 230 volt rated motors are suitable for use on 208 volt systems. The voltage drop will make this problem worse.
Don

[This message has been edited by resqcapt19 (edited 12-13-2005).]


Don(resqcapt19)
Re: suggested wire size #59703
12/13/05 10:17 PM
12/13/05 10:17 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Don is quite right; even under the best of conditions, you're really pushing it when you try to run a "230v" motor on 208 volts.

As a general rule of thumb, a motor may be used at plus or minus 10% of the nameplate marked voltage. So if your nameplate avtually reads simply "230v", then it should have a minimum of 207 volts at all times- and make sure that value is measured "under load!"

Now, if the motor is marked 220, or 208/230, etc...well, you get the picture.

I would also be very conservative in allowing for voltage drop. Remember, motors- especially those used in compressors- have a considerably higher curent required for starting; you almost want to base your voltage-drop calculations on the "LRA", or 'locked rotor amps.'

An exhaust fan isn't really fighting a load as it is starting up; so the inrush current needed isn't as great as it might be in other applications. You will probably be able to use #8.

One thing to also consider is a motor satrter with electronic overloads ("heaters"). Even though strictly not necessary, it will provide additional protection for the motor. The electronic elements provide protection against many other power problems than simple 'heaters' do.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,305 Are you busy
187,944 Re: Forum
177,473 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.032s Queries: 14 (0.004s) Memory: 0.9927 MB (Peak: 1.1513 MB) Zlib enabled. Server Time: 2018-10-17 01:40:33 UTC