If you have one service that is split in two, doesn't the service panels have to be grouped together in one location?


Dnk....

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#59551 12/07/05 08:32 PM
Joined: Dec 2003
Posts: 751
E
Member
If they are in the same building, yes. Separate buildings, no. Think of what the power company does for a row of houses.
I assumed from the wording of the original post the garage was separated from the house. If it is attached, then only the CB feed is allowed to a remote panel location.


Earl
#59552 12/07/05 08:47 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
I would see a problem with placing 300 amp's worth of main breaker on a feeder sized for 200. Use the breaker.


Not feeder, service entrance conductors. [Linked Image]

This is done quite often in multi family dwellings, as long as the conductors are rated for the calculated load.

230.90 Exception No. 3.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts