ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 59 guests, and 5 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#59540 12/07/05 09:21 AM
Joined: Nov 2004
Posts: 80
B
Bert66 Offline OP
Member
is it acceptable to use split bolts to connect from the primary side of a main breaker to service another main breaker in a seperate panel. let me explain, from the meter socket we feed a 200a main breaker panel, an additional garage was added with a 100a main breaker panel. could i use split nuts to terminate and supply power to the second panel or just put another 100a breaker in the first panel to feed the second 100a main breaker in the second panel? In this configuration both panels would have a paralle feed from the meter. Does this violate any code?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#59541 12/07/05 09:51 AM
Joined: Jun 2004
Posts: 220
T
Member
I would put another breaker in the main panel and feed out to the garage. you would save time and IMO have a more secure connection. Is there some reason you wanted to do it this way, like no more spaces in the main panel? As far as violating any code, I would want to know how far from the main it is, you might be able to use the tap rule.

[This message has been edited by trekkie76 (edited 12-07-2005).]

#59542 12/07/05 10:15 AM
Joined: Jun 2001
Posts: 161
M
Member
I've been having a brain block on this one... When you run wires from the meter to the building main breaker it is called a service conductor, right? What is the wire set called when you run from a new 100A breaker in the main panel to another building, as in the suggestion from trekkie76? Feeder? Lateral? Branch circuit conductor? I want to find out to apply the proper rules from the code to see if I can run them inside or if I need 2" concrete or keep them outside...
(Some days there's just too many pages in the code... ;-)


Mike Wescoatt
#59543 12/07/05 10:16 AM
Joined: Feb 2005
Posts: 693
L
Member
I would see a problem with placing 300 amp's worth of main breaker on a feeder sized for 200. Use the breaker.


Larry Fine
Fine Electric Co.
fineelectricco.com
#59544 12/07/05 12:46 PM
Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
Any connection on the line side of the service disconnect is a service entrance conductor and would have to follow SE rules. It also adds to the size of the service as Larry points out.
Installing this as a feeder (on the load side of the service disconnect) is a safer option with less potential problems.


Greg Fretwell
#59545 12/07/05 01:44 PM
Joined: Jan 2005
Posts: 91
H
Member
I think that code section that your question refers to is 230-40 exception #1.

You've given us breaker sizes but I'm curious about the calculated or actual loads served by both panels - 230-23 (a) & 230-31(a).

Another approach would be to come off the load side meter lugs. While permissable you won't have the added piece of mind that having a CB on the conductors would give you.



[This message has been edited by Helectric (edited 12-07-2005).]

#59546 12/07/05 03:53 PM
Joined: Dec 2005
Posts: 64
J
Member
Where are you planning to find a meter with lugs rated for more than one wire?

The biggest concern I would have is stripping the current wires to attach that split bolts as they are live.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#59547 12/07/05 04:06 PM
Joined: Aug 2001
Posts: 335
S
Member
jwhite:
I did one that had a 400a meter can, 350 Cu thru the mast to the POCO. In the meter can we removed the single lugs and put in doubles. We fed two separate panels, one in the house and one in a garage. AHJ had no prob with changing the lugs. (in that area the homeowner owns the meter can, it's not provided by POCO)

#59548 12/07/05 06:23 PM
Joined: Jan 2005
Posts: 91
H
Member
JWhite & Steve,

Yes, this is done in my area as well. I think that you can even order meter cans with studs only and then install the desired lugs yourself.
If I remember correctly, the code allowed this practice until the 70's then it was taken out for about 24 years. I'm not sure but I think it (230-40 exception #1) first reappeared in the 2002 code.

[This message has been edited by Helectric (edited 12-07-2005).]

#59549 12/07/05 08:00 PM
Joined: Dec 2003
Posts: 751
E
Member
If you tap the service conductors ahead of the main, these are still service conductors, and are subject to all the rules of services. You cannot run service conductors through building #1 to feed building #2. (230.3) Either make your connection outside the building (10x10x4 J-box) or feed through a CB, as discussed.

[This message has been edited by earlydean (edited 12-07-2005).]


Earl
Page 1 of 2 1 2

Link Copied to Clipboard