Joined: May 2002
Posts: 1,716
R
Member
Makokiller, can you give an NEC reference to where it is required to have a #4 to the rod or rods?

Might you be thinking about a local code?

Roger

Horizontal Ad
Joined: Dec 2004
Posts: 51
M
Member
look at the chart 250.66 he said that he has a 200amp service.. do the math

Joined: Jan 2003
Posts: 4,391
I
Moderator
Mako take a look at 250.66(A) and do the reading. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: May 2002
Posts: 1,716
R
Member
Mako, as with any part of the NEC you must read the whole article, you can not stop at one section or table.

Quote
250.66 Size of Alternating-Current Grounding Electrode Conductor
The size of the grounding electrode conductor of a grounded or ungrounded ac system shall not be less than given in Table 250.66, except as permitted in 250.66(A) through (C).

Here is the kicker.

Quote
250.66(A) Connections to Rod, Pipe, or Plate Electrodes Where the grounding electrode conductor is connected to rod, pipe, or plate electrodes as permitted in 250.52(A)(5) or (A)(6), that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than 6 AWG copper wire or 4 AWG aluminum wire.


Roger

Joined: Dec 2004
Posts: 51
M
Member
so let me get this straight.. you could use #6 copper for your city water pipe connection, and your ground rods??? even for lets say a 300amp service??

Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
so let me get this straight.. you could use #6 copper for your city water pipe connection, and your ground rods??? even for lets say a 300amp service??

To the rod yes, to the water line it would be sized directly from table 250.66.

Put a 4000 amp service in a field and you will only need a 6 AWG CU to one or two ground rods.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Dec 2004
Posts: 51
M
Member
now that is what i thought.. when do 300 amp services, I run #4 to the rod and #2 to the water meter, and thanks, with the price of copper nowadays it will save me some money..

Horizontal Ad
Joined: May 2002
Posts: 1,716
R
Member
Mako, as Iwire points out, which is the point of this thread, the connection to the rod(s) only need be a #6 copper regardless of the size of the service.

In this thread the water piping is not part of the GES.

Roger

Joined: May 2002
Posts: 1,716
R
Member
Mako, sorry, you posted while I was typing.

Roger

Joined: Apr 2003
Posts: 13
B
Member
I think you need to bond the water line ( Key Word ) and ground 2 rods

Page 2 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
551,659 Are you busy
426,207 Re: Forum
396,888 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5