Raceway bonding #59194
11/29/05 07:11 PM
11/29/05 07:11 PM
Q
qopanel  Offline OP
Member
Joined: Jul 2002
Posts: 17
My boss and I are having a disagreement with the sizing of a raceway bond. We have a 600amp service, with Parallel 350's fed underground to a distribution panel through pvc. I,m saying we need to have 1/0, and he is telling me #1. I'm a little confussed on where to find the sizing of this conductor. Should it be based on 250.66?

Work Gear for Electricians and the Trades
Re: Raceway bonding #59195
11/29/05 07:21 PM
11/29/05 07:21 PM
Q
qopanel  Offline OP
Member
Joined: Jul 2002
Posts: 17
Never mind....I had a brain fart and forgot to look a little further...250.122. I lost. Now I owe the boss lunch.

Re: Raceway bonding #59196
11/29/05 08:27 PM
11/29/05 08:27 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Now you've got me confused. Why are you bonding PVC? If the parallel 350's were copper and in a metal conduiit, the bonding conductor would be 2/0.

Or, are you bonding a conduit that is after the service disconnect & overcurrent device?

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: Raceway bonding #59197
11/30/05 08:04 PM
11/30/05 08:04 PM
Q
qopanel  Offline OP
Member
Joined: Jul 2002
Posts: 17
I am bonding heavy wall conduit stubbed down, then changing to pvc underground, then back up in heavy wall again. And yes it is after the overcurrent device.

Re: Raceway bonding #59198
11/30/05 08:54 PM
11/30/05 08:54 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Yup, you owe the bossman a lunch. You going to get him something good?


Few things are harder to put up with than the annoyance of a good example.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,100 Are you busy
185,547 Re: Forum
174,846 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9669 MB (Peak: 1.1050 MB) Zlib enabled. Server Time: 2018-07-17 11:24:37 UTC