#58573 - 11/12/05 08:52 PM Hot Tub GFCI Breaker 240v  
Cinner  Offline
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
I am doing a 40 amp 2 pole gfci breaker install for a hot tub that needs only 240v. The gfci breaker has 2 neutral terminals which I understand, but in this install there is no neutral needed. Will the gfci monitor an imbalance b/w the 2 hots?


Work Gear for Electricians and the Trades

#58574 - 11/12/05 09:06 PM Re: Hot Tub GFCI Breaker 240v  
stamcon  Offline
Member
Joined: Mar 2001
Posts: 329
So San Francisco CA
If the tub manufacturer states a grounded conductor(neutral) is not required, connect the line side white wire on the breaker to the neutral bus and leave the load side neutral terminal empty. The breaker will work as designed.

steve



Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.003s) Memory: 0.7437 MB (Peak: 0.8590 MB) Zlib enabled. Server Time: 2017-10-23 02:33:32 UTC