ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Furnace igniter leaking noise to stereo
by Haligan. 05/21/18 03:28 PM
480 Delta
by ghost307. 05/21/18 10:38 AM
turning down possible problem customer
by HotLine1. 05/21/18 07:53 AM
electircal ageing test on IPC
by HotLine1. 05/14/18 09:42 AM
What estimating software do you recommend?
by wattsittoyou. 05/14/18 06:28 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 25 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Coleman 5kw generator question #58199
11/02/05 03:47 PM
11/02/05 03:47 PM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
My customer has an older Coleman 5Kw Powermate PM0525202.

Problem is that the receptacle is different - it's got a 6-20R rather than an L14-20R (one flat and one 90deg rotated blade vs. 4 prong twistlock). I checked the Coleman site - no schematic. I assume the neutral and the GND are bonded inside the unit. There is a separate 120 v duplex on the unit.

Has anyone ever changed out the receptacle so the neutral and GND are brought out separately. I plan to back-feed the panel with a Square D interlock.

Thanks for help!

Work Gear for Electricians and the Trades
Re: Coleman 5kw generator question #58200
11/02/05 09:20 PM
11/02/05 09:20 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
Coleman says it should have a twistlock. Are you sure that is the right model number?


Greg Fretwell
Re: Coleman 5kw generator question #58201
11/02/05 09:58 PM
11/02/05 09:58 PM
D
davemica  Offline
Member
Joined: Oct 2005
Posts: 12
florida
If you are talking about the 3 wire 240v receptacle on that generator, check carefully, as I'm pretty sure there is no midpoint neutral just straight 240v.

Re: Coleman 5kw generator question #58202
11/03/05 01:28 AM
11/03/05 01:28 AM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
Yup, sure of the model # - it's an older model; current models have the 4 conductor twist lock.

My custoer's unit has what appears to be 2 duplex receptacles, one marked 120V and the other marked 240V - a 5-20R and a 6-20R. Tells me there's got to be a neutral somewhere......

Re: Coleman 5kw generator question #58203
11/03/05 03:00 AM
11/03/05 03:00 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
You could meter it out. If the neutral is bonded you should see 0 ohms between the neutral and ground on the NEMA 5-15s and the ground on the 6-20. To be connected properly your transfer equipment should also be switching the neutral.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,857 Are you busy
184,210 Re: Forum
173,451 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9674 MB (Peak: 1.1058 MB) Zlib enabled. Server Time: 2018-05-22 04:10:31 UTC