#58177 11/01/05 07:10 PM
Joined: Dec 2001
Posts: 300
M
Member
We're building alot of small computer server rooms in all fo the schools in our district.

Each of these is nearly identical and needs a specific number of 120 and 208V recepticles. We've only done a couple so far and pulled each circuit from nearby panels but some weren't all that nearby.

With more than a dozen to go, I got the brilliant idea of installing a small subpanel in each server room. this means pulling less wire and gives easy room to expand in the future.

I need a small three phase electrical panel. The ideal panel would be 60A with 6 breaker positions but something a little larger would work. I'm not so concerned about size (although in some of these closets it is a problem). I'm mostly concerned with capacity. I don't have an available 200A near some of these locations.

The smallest panel I've seen is a 100A 24 position - Much more than I need.

Anybody know of a smaller one?

Horizontal Ad
#58178 11/01/05 07:56 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
How about buying the 100A and replacing the main with a 60A that you buy separately?


Ron
#58179 11/01/05 08:58 PM
Joined: Apr 2002
Posts: 7,413
Likes: 8
Member
M-GUY:
Square d
QO403L60NS; 3 CIRC, 60 AMP, MLO
QO312L125G; 12 CIRC, 125 AMP, MLO

Both are main lug only panels.

John


John
#58180 11/02/05 01:03 AM
Joined: Jun 2003
Posts: 681
P
Member
Why does he need a main. Use the 100 main lug panel and supply it with whatever size overcurrent device ahead of it, as long as the device is not more than 100 amps.


Pierre Belarge

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 70
Joined: January 2002
Top Posters(30 Days)
Trumpy 4
triple 3
dsk 1
Popular Topics(Views)
520,603 Are you busy
402,459 Re: Forum
375,469 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5